Good Morning ,

I'm working on a safety project , and I'm thinking of using the
Guardmaster 440C-CR30 Software configured safety relay with the 440C-ENET Guardmaster Ethernet Plug-in module.

I would like to present the status of the safety circuit on a HMI. Does the 440C-CR30 allow to interface with a Panelview Plus HMI ? and what software do you use to to configure the 440C-CR30 ?

Thanks so much,
 
I haven't used these yet, but I've seen several demos. Connected Components Workbench is used to program the 440C-CR30 relays. And yes, you can pull the info into a PanelView Plus for status display. The demos I've seen use the Ethernet plug-in module but I don't really have any technical details.
 
Thanks ,

On a Panelview Plus , you can bring into the application , numerous PLC's as shortcuts and display information from each one , correct ?

If the PanelView Plus is connected via Ethernet to multiple controllers, then yes, you should be able to create a shortcut to each controller and pull data from them. I can't recall if there are any limits to number of shortcuts per application.
 
Sorry, I'm not a big fan of it. Used it some time ago.

Just ensure your components connected to it are safety rated. There are dedicated outputs which checks for components configured in place, by means of pulses output to it. I had a contactor and a valve bank power, connected to it, which gave out intermittent errors.

Regards
 
I've used that arrangement along with a non-safe PLC. Via Ethernet/IP, the PLC could monitor everything and the safety controller had non-safe inputs that the PLC could write to for clearing faults and resetting safety circuits. I don't see why an HMI could not do the same.
 
You've gotten many answers, but I still wanted to add some info:

1. I would use a "master" or "line" PLC to pull in all of the data from all your safety devices.

2. I would create a single link from this PLC to the HMI which needs to have this information displayed.

3. If you need to display this data on multiple/different HMIs, I would create a produced/consumed or MSG based message from the "master" PLC to those who needed it and link to the data this way.

Also, the "standard" PanelView HMIs only allows a single reference point (it's very frustrating), so unless you have the more expensive "performance" edition, you may not be able to link to multiple PLCs.

Hope that helps...
 

Similar Topics

I have a Samsung Galaxy book go 5g it has windows 10 and a Arm processor. I have been trying to download the CCW software and it won't download...
Replies
3
Views
1,979
Good Evening , What are some of the options that Rockwell Automation have now to purchase software , Studio 5000 , RS Logix 500 , RS Logix...
Replies
9
Views
4,728
Good Evening , I'm possibly going to be taking over a automation service department . I would like to get all the Rockwell Software that I...
Replies
16
Views
6,590
Hello, is anyone running FactoryTalk View ME v11 on the same computer running Studio 5000 v30 and below. When I installed the FTV software the...
Replies
3
Views
2,219
Good Morning , I'm getting ready to take the step of retiring our Windows XP laptops. We have a number of older ControlLogix CPU's and...
Replies
35
Views
9,555
Back
Top Bottom