Hi,
We have a project to replace one Star Delta connection for 90kw motor (3 phase, 415V) with an Inverter. Before dismantle the S/D, the current before the contactor is around 80Amp, after replacing with an Inverter, we measure the same incoming cable (before Inverter), the current is only 18Amp. We measure the cable after the Inverter, the current is 68Amp, is that possible that the incoming current (before Inverter) is so low?
The speed is the same (full).
Thank you.
We have a project to replace one Star Delta connection for 90kw motor (3 phase, 415V) with an Inverter. Before dismantle the S/D, the current before the contactor is around 80Amp, after replacing with an Inverter, we measure the same incoming cable (before Inverter), the current is only 18Amp. We measure the cable after the Inverter, the current is 68Amp, is that possible that the incoming current (before Inverter) is so low?