Trying to set up a Logix 5000 L73 controller so the customer's Ovation DCS can read some analog and digital values at specific addresses. I think this involves CIP data, and I see several example of 2 PLCs talking to each other by external controller tag names.

But, I'm not sure how to make available controller tag values at a specific address (Example: customer wants to read bits at N7:200-209).

Is this a common task... any examples out there? Thanks.
 
I've worked on the Logix side of this, we just place the data into tags (e.g. SamplePLCData[X]) and I believe the Ovation pulls from the Logix PLC. I haven't dealt with the Ovation side of it, so I can't really comment on it, but as far as the Logix is concerned, it's been pretty simple in my experience.


In my application, we were using MSG instructions. So the DCS would write into one ControlLogix ("Integrator" PLC) in the addresses SamplePLCData[59]-SamplePLCData[74] (for example) which would then write to a ControlLogix on the plant floor in addresses PlantPLCData[0]-PlantPLCData[15] and control the process. The Integrator would then read data from the plant PLC and place it into SamplePLCData[75]-SamplePLCData[78] which would then be read by the Ovation. Long story short is that you can name the tags whatever you want as long as the DCS is configured to look at the correct tags. I assume in your case that it would be N7[200]-[209], instead of SamplePLCData[200]-[209] in my case.
 

Similar Topics

Hi Iam using monitouch hmi(V9 soft) with omron plc cj2m (CX programmer). In this I want to read a data from hmi to plc. The data was like...
Replies
0
Views
111
Dear Experts, Please, kindly guide me through how to read data from ABB PLC to S7-1200 Siemens PLC. I want to use Siemens S7-1200 PLC to read data...
Replies
1
Views
460
Hello everyone, I'm working with an old ACM3710 device and I'm encountering an issue with the data frames I'm sending over an RS232 connection...
Replies
5
Views
693
Hi All, I need to read some data from a Rockwell 5380 PLC to a schnieder m340 PLC. What hardware will i require for both systems? on the M340...
Replies
12
Views
5,310
We have a Siemens CPU1511-1PN. This is a network with a CPU, HMI and 3 drives on Profinet. I want to connect this plc also to another ip-range...
Replies
7
Views
1,918
Back
Top Bottom