i think, i should use selector switch with 3 state to disconnect main contactor in transition from auto to manual. i used 2 state.


That would not change the above suggestion to use some sort of debounce
logic. Again, if I understand your problem.
 
i think, i should use selector switch with 3 state to disconnect main contactor in transition from auto to manual. i used 2 state.


I wouldn't recommend a software patch for a hardware design flaw. Simply wire your HOA selector switch so that the PLC output is isolated from the load when you switch to manual mode.
 
Something like the this:

6Lbxom1.png
 
Why not have the selector switch send both AUTO and MANUAL signals to the PLC as two inputs, and use the PLC output as the power for the contactor in both AUTO and MANUAL modes. Use the PLC logic decide how the output comes on if AUTO input is on or if MANUAL input is on.
 
There are more that one way to achieve the result you need.
What Mark says is also correct.

You can install an additional contact and use it to signal a DI but then you will have to do software modifications as well.
YMu9YiM.png
 
thanks everybody, specially Mark and JRB for very very good solution. you changed my bad decision.
 
Last edited:
Why not have the selector switch send both AUTO and MANUAL signals to the PLC as two inputs, and use the PLC output as the power for the contactor in both AUTO and MANUAL modes. Use the PLC logic decide how the output comes on if AUTO input is on or if MANUAL input is on.


One typically desires for the motor to be operational when the PLC is not available, if an HOA selector switch is installed.
 
You're right Bit Bucket, and so is everyone else. It all depends on exactly what smsebnaa wants to do.

I hope smsebnaa keeps that in mind.
 

Similar Topics

Hello everyone, been awhile since I've posted..... As the title suggests, using Crimson 3.1 software (Red Lion) I cant seem to figure out if its...
Replies
4
Views
1,726
Hi, Just wanted some thoughts on protecting control and instrumentation from welding damage. We had a PLC and drive fail after some welding work...
Replies
12
Views
5,060
Hi Everyone, Yesterday we encountered an issue where I had a 480V 3Ph 2HP Powerflex 525 blow up. Upon further inspection, we noticed that 10...
Replies
21
Views
6,091
Hi, I am currently developing a project and need to know if it's possible that once I download to CPU and HMI no one can upload it and re use the...
Replies
23
Views
6,929
We have a PV+400 on our floor that has something quite odd going on. The program hasn't been changed in quite a while, at least a couple of...
Replies
8
Views
5,453
Back
Top Bottom