PowerFlex 525 not Running

larbi16

Member
Join Date
Dec 2023
Location
Dallas,Texas
Posts
15
Hi I got a powerFlex 525 AC Drive (used) i changed parameter t053 to 2 to do factory reset and now i have both parameters 46 and 47 on 1 but cant put the drive on RUN mode.
any help would be greatly appreciated.
 
You probably need to zero out all of the digital inputs, T62, T63, T65, T66, T67, T68 or set them to what they are used for. You may also need to jumper the S1 and S2 to S+ for the safe off option. If it's used they may have pulled out the factory default jumpers.
 