PowerFlex 525- CompactLogix Tags does not include Output Current of the Drive.

Join Date
Aug 2016
Location
Virginia
Posts
343
Good Morning ,

I am working on a project with some PowerFlex 525 drives. I am using CompactLogix 1769-L18. I took notice that the tags that populated in the PLC does not include Actual Current. I am surprized that it does not . Is there a way you can capture the actual current that the motor is driving from the drive , thru ethernet ?

Thanks so much in advance ,
 
I think when you add the drive to your IO tree and you get the New Module window, on the first tab (General) if you click the Change button it will give you the ability to add the current to the tag that is created.
 
Last edited:
I'm not that familiar with 525 drives? Do they support datalinks? That's one way. Or you can use explicit messaging, I believe.
 
like Archie said, you can add the tag when creating the device.

also, you can add the tag offline, then going back online will prompt the change/download dialog
 
Thanks for the information. I never took notice of that before. So while offline I select what information from the dropdowns , and check " Display as Tag Members " and then I download to the processor , correct ? Then when I go into "Controller Tags" , they should be listed in the same tag list under that drive ?

Thanks ,
 
I just did it , and they are not in that drive tag list. This what what I did....

-I opened properties for that PowerFlex 525. Clicked "Change".
-Selected Output Current , DC Bus , and Output Voltage. Checked "Display as Tag Members. Clicked OK. Saved.
-Downloaded to processor. Went back into run . Drilled down into the Drive Input Tags , and they are no where in sight . I opened the drive properties while online and the dropdown list boxes , that I selected , say disabled .

What do you think I did wrong ?

Thanks in advance for your help .
 
When you made the change and pressed OK, you should have had a dialog box pop-up that says" These changes will cause module data types and properties to change. -I/O parameter selections. Change module definition?" You have to press "Yes".
 
Sorry. I had the RS Logix 5000 not full screen and did not see the OK on the properties window , I just closed the window with X. Those tags are now in the tag list.

But now I cannot communicate with Drive. Now I have this fault on this drive...

( Code 16#0110 ) Connection Request Error. Module Not Configured .

What in the world caused this ? :) I thought I just added these tags .
 
I'm sorry. I'm a idiot. I went offline then seen the option to download. Now it comes up saying that the drive is V. 5.001 and the project is 4.001 and that they may be errors if I download.
 
You lost communication with the drive because the PLC configuration no longer matches the drive configuration...

In the PLC, you just set the first Input Datalink to be "Output Current", but on the drive, it's still set to "Nothing".

If you update that parameter on the drive, you'll be away.

There are probably several ways of doing it - from the PLC, from the drive itself, from CCW, but the important thing is that, however you achieve it, the parameters in the drive match your PLC configuration exactly
 

Similar Topics

Good Morning , I'm working on a project that I may need to change the acceleration rate according to which recipe is being ran. I took notice...
Replies
2
Views
2,260
Good Morning , We have been running a machine , PLC and PowerFlex 525 for over a year. For some unknown reason , I have a Yellow Triangle on...
Replies
9
Views
4,528
Good Afternoon , I am working on a project on the desk , and I am getting DC Bus Voltage , Current , and Fault Codes from my PowerFlex 525 to...
Replies
4
Views
6,702
PowerFlex 525 - can you access the parameters from a MicroLogix 1400 & CompactLogix Good Morning , I have a separate stand alone machine...
Replies
2
Views
3,351
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
0
Views
6
Back
Top Bottom