Power Calculations For An Industrial Control Panel

rustydud

Member
Join Date
Mar 2011
Location
USA
Posts
40
Hello everyone, and thanks in advance for viewing.

I have an industrial control panel that is powering a VFD, pilot lights, relays, digital panel meters, and some other devices. There is one(1) power feed powering the panel: it is 460VAC, 3-phase from a motor control center (MCC) bucket.

The panel contains the following:

  • (1) VFD. It is 460VAC, 3-phase and is running a 20HP pump.
  • (1) 500VA transformer for transforming 460VAC, 3-phase to 120VAC, 1-phase. A few loads in the panel are 120VAC, 1-phase.
  • (1) 24VDC power supply that is powered by the aforementioned 120VAC, 1-phase. Several loads in the panel are 24VDC. 24VDC loads include pilot lights and digital panel meters.

I know how much current / power each device draws - I have this information readily available.

Suppose you are asked to calculate the power usage of this panel. I am looking for the proper method to do this. What is the proper method for calculating the power usage of this panel?
 
With a panel FLA - you can calculate the Watts/kwh/etc.

IMO, ignore all the 120VAC and 24VDC - they are powered by a branch of 480VAC in your application. You do need to calculate them to get the transformer size - and you should oversize the transformer to make sure you have room to add if necessary.

Just calculate the 480 loads - which for you are:
20HP motor - 27A FLA (per NEC chart)
500VA Transformer - about 1/2A at 480VAC

Generally, you want the largest load (20HP motor - so 27A) listed on your main panel tag along with the total load ( ~ 27.6A). I don't typically build UL panels - so I'm a little grey on the UL portion - I believe they want the actual NEC chart value and not the actual calculated value.

Personally, I would size this panel with a 100A disconnect, fused at 70A, (60A for the motor) in case any additions happen in the future. If you are sure there will be no additions, you could fuse at 60A with a 60A disconnect.

(my values are from Bussman's SPD - if using other manufacturers or breakers, these numbers don't work)
 
With a panel FLA - you can calculate the Watts/kwh/etc.

IMO, ignore all the 120VAC and 24VDC - they are powered by a branch of 480VAC in your application. You do need to calculate them to get the transformer size - and you should oversize the transformer to make sure you have room to add if necessary.

Just calculate the 480 loads - which for you are:
20HP motor - 27A FLA (per NEC chart)
500VA Transformer - about 1/2A at 480VAC

Generally, you want the largest load (20HP motor - so 27A) listed on your main panel tag along with the total load ( ~ 27.6A). I don't typically build UL panels - so I'm a little grey on the UL portion - I believe they want the actual NEC chart value and not the actual calculated value.

Personally, I would size this panel with a 100A disconnect, fused at 70A, (60A for the motor) in case any additions happen in the future. If you are sure there will be no additions, you could fuse at 60A with a 60A disconnect.

(my values are from Bussman's SPD - if using other manufacturers or breakers, these numbers don't work)
I agree, but I’ll just point out that this only tells you what it MIGHT consume, worst case scenario. The motor will only pull FLA if DEMANDED by the load, but the load is king here. If someone wants to know the ACTUAL power being consumed then the answer can ONLY be “it cannot be calculated, it can only be measured”. Many VFDs will actually tell you the kW it is putting out, so add about 3-5% to that value as input losses within the VFD and CPT and you will have a workable number that means something.
 

Similar Topics

Trying to understand a power study done a few years back on one of our lines. It says there were volatge sags on one phase (277) that went as low...
Replies
4
Views
2,993
Here's something I've never had a problem with before. Just put together a new 10-slot SLC rack with a P2, 5/05, and eight NT8 modules. When I...
Replies
7
Views
5,243
I want to use an Induction AC motor to rotate a steel disc at about 100 RPM as a minimum speed. This steel disc is about 65.7cm in diameter, 2.5...
Replies
10
Views
7,473
We have a panel view 1000 powered by 230VAC protected by a 16A type 2 MCB. After initial power up of the MCC, the MCB trips and needs to be...
Replies
1
Views
28
Good morning, I'm searching for a power supply to convert 3 phase 480VAC to 120VAC and 24vdc. Is there an all-in-one power supply like this on the...
Replies
6
Views
114
Back
Top Bottom