Hi all,

I have a PLC5 rack that is actually full(No place for an aditionnal card). The rack has a couple of spare inputs on 1771-IFE cards and I need to hook up an instrument that requires a differential input.

Since AB documentation tells not to mix "singled-ended" and "differential" input configuration on the same card and all of them are configured as "single-ended", I was asking myself : Is there a way to connect a differential output instrument to a single-ended input using a converter or some kind of isolator ?

Thanks !
 
if the device supplies an isolated output you *may* be able to hook up it's common to the card common along with the other single ended commons. this may make it more susceptible to noise.
 
I was planning on using a ABB analog signal isolator.

Your answers confirmed me that it is the right way to do it.

Thanks !
 

Similar Topics

We have an old PLC5/25 with 6 racks spread over 4 cabinets. At some time past they tried to connect a DL20 ans 3 DL10 displays to it. The...
Replies
4
Views
1,917
As the title indicates I am trying to connect a PLC5/40C to Honeywell Experion R301 using 1785-ENET card. I am not really familiar with PLCs at...
Replies
2
Views
3,001
I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
Replies
4
Views
161
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
Replies
3
Views
379
Back
Top Bottom