Panel view1250 FW 5.10

Kipper

Member
Join Date
Sep 2014
Location
Belvidere IL
Posts
19
I have created a panel view screen that works perfectly in Factory Talk View Studio Machine edition Ver 8.20. I load it into a PV 1250 Ver 5.10, my digital displays will not function on the PV 1250 but work in FT on the computer. I have been playing with this for 2 days. Anyone have any idea as to what I could be doing wrong?
Thanks Kipp
 
Can you explain the exact details of "my digital displays will not function" ?

What objects don't work ? Do they wireframe, or show unexpected values ?

Is the problem limited to individual objects, or whole displays full of them ?

I like to create a diagnostic Display with a full-size FactoryTalk Diagnostic display object on it, so I can see whatever error messages the various FT services are generating.

The most common "it works on my PC but not on the terminal" situation is when the communications Shortcut is not properly configured in the Runtime tab of RSLinx Enterprise. There will be communications timeouts and errors in the diagnostic list.
 

Similar Topics

I HAVE B&R POWEL PANEL 400 HMI. THE ISSUE IS HMI NOT BOOTING, DISPLY SHOWING CONTIUESLY (ATTEMPTING TO A BOOT HARD DRIVE....)
Replies
1
Views
50
Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
Replies
3
Views
92
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
229
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
Replies
8
Views
420
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
Replies
0
Views
98
Back
Top Bottom