hoguegregplc Member H Join Date Aug 2023 Location McKinney, Texas Posts 10 Sep 5, 2023 #1 Build error occurs with TON ladder logic command. Time Input expected on block. Using Integer Tag under Control Local, and then hard number 19. Still can't build. I can't find any thing else to try.
Build error occurs with TON ladder logic command. Time Input expected on block. Using Integer Tag under Control Local, and then hard number 19. Still can't build. I can't find any thing else to try.
hoguegregplc Member OP H Join Date Aug 2023 Location McKinney, Texas Posts 10 Sep 5, 2023 #2 TIME data type The PT parameter of the TON must be a TIME data type in order to build. Use the AnytoTime command to convert from the HMI INT over Modbus TCP/IP.
TIME data type The PT parameter of the TON must be a TIME data type in order to build. Use the AnytoTime command to convert from the HMI INT over Modbus TCP/IP.
drbitboy Lifetime Supporting Member Join Date Dec 2019 Location Rochester, NY Posts 8,159 Sep 5, 2023 #3 Nice, thanks for the feedback, Greg.