Megging a 3ph 30hp motor. Run by a PF753 showing F13 ground fault. Getting 15K Ohms @ 1000v with megger. Yes Komhs. Bad motor correct? Should be like pry .5Mohm or higher if I remember correctly, been awhile. Motor require crane for replacement, so trying to be sure.

Thanks.
 
Hi, James and welcome to the forum.
Most of the time in motors I was taught to use a rule of thumb of "1 megohm per volt of line voltage". So, 500 Meg ohms per phase on a 480 V motor. As long as I've had that or above, then I will leave the motor in service. Hope this helps.
 
First never ever meg a motor connected to a vfd or any other drive, you can damage the drive they are not designed for that level of voltage any number of things could be damaged.
if the reading you got are correct I agree the motor I bad needs repaired or replaced.
do the absorption test it the best way to check faulted motor.
if as you say the motor is located in a bad location then I would separated the motor from the wiring at the motor box and meg both the motor and the wiring separately just to be sure you don't have bad feed wire .
Also I think you 1000V test is to low I was told the rule of thumb was 2 x the rated voltage + 1000V the next level up, that would make the megger test voltage 2500V I would opt for 5000V with a 480v motor but that's just me.
in your case it may be cheaper just to replace it with a new motor over repairing it. The cost of the crane twice verses once.
 
Our motor shop standard is 2000V on the meg test on 480V motors and down.

I once had a motor that was tripping the vfd out of ground fault. The electrical contractor was testing it with some megger and couldn't get it to fail and didn't understand why the drive was tripping out. Called us in and I put our high voltage computerized winding tester on. The motor failed the meg test at around 1400V. The contractor had only been doing a 1000V test which he thought was good enough for a 480V motor. Drives seem to be sensitive and can pick that up quick.
 
The motor was megged with phases disconnected from the vfd. I megged from the output of vfd to motor and also at the motor peckerhead. I knew i was right, but was second guessing myself with the severity of the situation due to it's location. I've always assumed that our 1000v megger was good enough, but looks like I'll have to find a new one. New motor and a crane on the way. Thanks guys, love these forums!
 
if you are looking for a megger have a look at AEMC and look at the 5000V units
I think that 2000 / 2500V is to light to check a 480V motor
they may not be cheep but they are the best.
 
Gentlemen, please consider that both ANSI and NEMA spec 1000V meggars as proper for field testing of used induction motors. Also, consider that a brand new non-MG1 Motor is tested with 1200VAC at the factory and an MG1 motor is tested at 1800v DC pulse power.

Testing a motor with an insulation system designed for 480VAC at levels above 2000V can be expected to damage perfectly good insulation and convert a good motor to bad simply by testing it.

Finally, expecting to see 1000000 times the nameplate voltage as the lowest acceptable meggar test resistance is way off. It isn't unheard of for a new, bone-dry motor to test less than that.

The general rule I've seen most commonly at 480VAC is at least 1000000 ohms to ground and, when possible to test, phase to phase. Less than that indicates a motor recondition is needed and maybe even a rewind. It depends how high the resistance goes after a good cleaning and bake-out.
 
Gentlemen, please consider that both ANSI and NEMA spec 1000V meggars as proper for field testing of used induction motors. Also, consider that a brand new non-MG1 Motor is tested with 1200VAC at the factory and an MG1 motor is tested at 1800v DC pulse power.

Testing a motor with an insulation system designed for 480VAC at levels above 2000V can be expected to damage perfectly good insulation and convert a good motor to bad simply by testing it.

Finally, expecting to see 1000000 times the nameplate voltage as the lowest acceptable meggar test resistance is way off. It isn't unheard of for a new, bone-dry motor to test less than that.

The general rule I've seen most commonly at 480VAC is at least 1000000 ohms to ground and, when possible to test, phase to phase. Less than that indicates a motor recondition is needed and maybe even a rewind. It depends how high the resistance goes after a good cleaning and bake-out.


DickDV, 1,000,000 ohms phase-to-phase?or do I misunderstand you?

In my opinion, 1000V may be good for most circumstances but it may not catch everything. But I would agree that 5000V seems very excessive.
 
I believe that table on p.17 is the same or very similar to the charts that EASA produces
 
lesmar. that is one million ohms phase to phase or phase to ground. Of course, you can't test between coils that are internally connected.


These guidelines are for FIELD testing. There are other potentially higher voltage tests that are intended for SHOP use.
 
To clarify, when I said phase-to-phase I meant from one coil to another. Clearly, that would only be meaningful if you can isolate the coils with the leads available in the junction box. Coils tied together with connections made up inside the motor and not available in the junction box cannot be meggared since they are already shorted together. They have to be treated as one coil for testing purposes.

Sorry for the confusion on that.
 

Similar Topics

I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
Replies
9
Views
219
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
309
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
162
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
365
Hello all, In my facility we have multiple 3HP 460V motors that are being controlled by VFDs which drive conveyor belts. The drives are randomly...
Replies
2
Views
227
Back
Top Bottom