We have a customer that wants to monitor current on all the 480v motors on a piece of equipment - 5-6 motors, all 5 HP or less. Ideally, I'd like to find something with Ethernet/IP comms to eliminate adding another analog input card to the PLC, but that's not necessarily required. We could just put VFD's on everthing, but that seems like overkill and cabinet space may be a bit of an issue. I looked at the AB E300 overloads, but those look to be about the same price as just using a VFD. Current doughnuts and a transducer are an option, but I was hoping there was a more elegant solution.
 
Current transformers with integral 4-20 mA transmitters are ubiquitous.
Forward the 4-20 mA signals to a local Ethernet/ip i/o node.
It is the way it is done, you use standard components, it does not cost an arm or a leg, it does not require much space. Elegant enough for me.

The "monitoring relays" that can be networked are usually bulky, require transformers on all legs, and are just way overkill if you just want to monitor 1 phase via your PLC.
 
What's the purpose? Monitoring current alone has its uses, but remember that current will fluctuate with voltage, not just with load. If you want to truly monitor load, you will get more useful information by monitoring kW, because that always represents the true shaft load on the motor. So for example if they want to monitor when a bit or blade is getting dull, do it with kW. If they just want to confirm that a motor is truly running, not just that the contactor is closed, then current is fine.

These guys have a nice line of retrofit current and/or kW sensors that use split core CTs so that you don't need to remove wires. You will see their distinctive blue color used in products sold by a number of other companies, they are the true manufacturer.
http://www.nktechnologies.com
 
What's the purpose? Monitoring current alone has its uses, but remember that current will fluctuate with voltage, not just with load. If you want to truly monitor load, you will get more useful information by monitoring kW, because that always represents the true shaft load on the motor. So for example if they want to monitor when a bit or blade is getting dull, do it with kW. If they just want to confirm that a motor is truly running, not just that the contactor is closed, then current is fine.

These guys have a nice line of retrofit current and/or kW sensors that use split core CTs so that you don't need to remove wires. You will see their distinctive blue color used in products sold by a number of other companies, they are the true manufacturer.
http://www.nktechnologies.com


We have a customer that wants

This is normally the point common sense goes out the window!
 
Current transformers with integral 4-20 mA transmitters are ubiquitous.
Forward the 4-20 mA signals to a local Ethernet/ip i/o node.
It is the way it is done, you use standard components, it does not cost an arm or a leg, it does not require much space. Elegant enough for me.

Cheap and easy, where's the fun in that? :)
 

Similar Topics

Hello, I was wondering if anyone got any suggestions for equipment that might be used to determine if a motor is running or not. Nothing too...
Replies
28
Views
5,471
Greetings from Michigan. I have an application where we want to monitor voltage and current coming off the output side of the AC motor drive. We...
Replies
12
Views
4,989
Motor control advice, I've been programming a transfer system that transfers parts from one station to the next. The FWD and REV travel is...
Replies
51
Views
28,581
HI i have a delta VFD M-series in the manual, in order to enter the motor rated current you set the parameter P,52 =the motor rated current my...
Replies
7
Views
690
Hey guys. So I have a 50 HP 460/600V motor on a PF525. I've verified the motor is wired correctly. The service factor is 1.15 and the pf is 0.8...
Replies
24
Views
1,937
Back
Top Bottom