leon78 Member L Join Date Jul 2004 Posts 65 Aug 16, 2004 #1 Where I can find Linear Measuring Ranges Table for Modicon TSX Quantum 140ACI03000 module?
Sliver Member Join Date Feb 2004 Location Kingston, Ontario Posts 488 Aug 16, 2004 #2 according to catalog (2001) 140 ACI 030 00 Voltage input linear measuring range 1..5V Current input linear measuring range 4..20mA
according to catalog (2001) 140 ACI 030 00 Voltage input linear measuring range 1..5V Current input linear measuring range 4..20mA
Jim Dungar Member J Join Date Apr 2002 Location WI Posts 1,152 Aug 16, 2004 #3 Website is at www.schneiderautomation.com. The manual you want is Modicon Quantum Automation Series Hardware Reference Guide 840USE10000.
Website is at www.schneiderautomation.com. The manual you want is Modicon Quantum Automation Series Hardware Reference Guide 840USE10000.
leon78 Member OP L Join Date Jul 2004 Posts 65 Aug 17, 2004 #4 Sliver said: according to catalog (2001) 140 ACI 030 00 Voltage input linear measuring range 1..5V Current input linear measuring range 4..20mA Click to expand... What are Raw Value in the 3x registers for 4mA, 20mA, 1V, 5V?
Sliver said: according to catalog (2001) 140 ACI 030 00 Voltage input linear measuring range 1..5V Current input linear measuring range 4..20mA Click to expand... What are Raw Value in the 3x registers for 4mA, 20mA, 1V, 5V?
krk Lifetime Supporting Member K Join Date Aug 2004 Location Kent Posts 795 Aug 17, 2004 #5 The 3xxxx raw data value for both ranges is 0 - 4095
leon78 Member OP L Join Date Jul 2004 Posts 65 Aug 17, 2004 #6 krk said: The 3xxxx raw data value for both ranges is 0 - 4095 Click to expand... Thank you for help