It is first time we are working with CANOpen.
There is a task to control Siemens Micromaster430 from Modicon M340. We've got EDS from Siemens, connection seems ok.
LEDs are follow
M340 CPU
CAN RUN - green ON constantly
CAN RED - flashing constantly
LEDs on Micromaster430
if no datatransfer green ON constantly
if datatransfer green flashing
According to manual MM430 is in "Opeartional Mode"
But M340 shows state of MM430 in RED color - "Pre-operational" and there is an Error "Configaration Error" and
Communication state 16X0100
Bit 8=1: Indicates the task cycle is faster than the CANopen master cycle (outputs can be overwritten). To avoid overwrite, you are advised to set a longer task cycle time that the CANopen cycle. The cycle values are available in the words %IWr.m.c.59 à %IWr.m.c.61.
Inspite of error we can read SDO, but we can not read PDO.
Is there any ideas?
Thanks in advance!
There is a task to control Siemens Micromaster430 from Modicon M340. We've got EDS from Siemens, connection seems ok.
LEDs are follow
M340 CPU
CAN RUN - green ON constantly
CAN RED - flashing constantly
LEDs on Micromaster430
if no datatransfer green ON constantly
if datatransfer green flashing
According to manual MM430 is in "Opeartional Mode"
But M340 shows state of MM430 in RED color - "Pre-operational" and there is an Error "Configaration Error" and
Communication state 16X0100
Bit 8=1: Indicates the task cycle is faster than the CANopen master cycle (outputs can be overwritten). To avoid overwrite, you are advised to set a longer task cycle time that the CANopen cycle. The cycle values are available in the words %IWr.m.c.59 à %IWr.m.c.61.
Inspite of error we can read SDO, but we can not read PDO.
Is there any ideas?
Thanks in advance!