Do not use DrBitboy's code it does not work, he needs to modify it.
Here is another using indirect addressing to add up * average the values.
 
DR your code does not work, a constant float has to be E 0.1 corrected that this is the result


nice catch, I updated that post to be [E/P D420 E10 D472]

It's often a bit beyond me to do this stuff in my head.

Also, of we are going to use indirect, why bother shifting the data? wouldn't it be better to

-+-[< Z0 K0 ]-+-[MOVP K0 Z0]
+-[> Z0 K19]-+


SM412
-] [-+-[E-P D444 D424Z0 D444]
+-[E/P D420 E10 D424Z0]
+-[E+P D444 D424Z0 D444]
+-[+P Z0 K2 Z0]



? Although then there needs to be some initialization code, and the roundoff error could accumulate.
 
You have to be careful using the index registers "Z" in scan, they are used by other functions or if used elsewhere, the way to do it once per scan then save it to a register then restore it before use if that is the requirement, however, if in a for/next it just jumps back until the number of iterations have been completed. Not that it matters but just use the "P" function on the SM412 it saves a little processing rather than the P function version of all the shifts etc.
 
This is your version modified, did it in FBD (hate the ladder IDE too slow to add instructions).
Slightly modified to allow of saving Z index register.
but it works ok Not bad just in the head code :geek:

DR_Version.png
 
You have to be careful using the index registers "Z" in scan, they are used by other functions or if used elsewhere, the way to do it once per scan then save it to a register then restore it before use if that is the requirement, however, if in a for/next it just jumps back until the number of iterations have been completed. Not that it matters but just use the "P" function on the SM412 it saves a little processing rather than the P function version of all the shifts etc.






Good points! thanks.
 
Just remembered there are two instructions ZPUSH & ZPOP, these will save & restore the Z registers but in reality it does the same job but saves all the Z registers from 0-9.
 
This is why I like the GXWorks2 or 3, as it's IEC compliant you can use arrays & no need for Z register just a variable makes things a little clearer.
It does actually use the Z pointer registers but that is in the compiled code so you do not have to worry about them.

FBD Average.png
 
This is why I like the GXWorks2 or 3, as it's IEC compliant you can use arrays & no need for Z register just a variable makes things a little clearer.
It does actually use the Z pointer registers but that is in the compiled code so you do not have to worry about them.

Sweet!

One (minor?) inconvenience with the incremental approach I proposed is that there needs to be additional code to initialize the array elements and the average to zeros (or to the current value); that is not a problem when the code re-calculates the average from scratch from the entire array at least every every time a new value is added.
 
It's not a problem from initial start, all the registers are initialised, the array is actually D addresses so for example a float array[0..9] is say D400- D419
so 20 addresses, these (if set in project) are retentive, if PLC is powered down then back up they keep the data, so yes for 1 second it will retain the last average then after 10 seconds will be a true average, assume the machine is stopped i.e. no pressure, then it will decay to 0, same with starting as the pressure rises so will the average, but again it will take 10 seconds to stabilise, but then again so will the actual pressure as it ramps up.
The only problem is that every second the average pressure will jump + or - rather than every scan, but the averaging process will tend to smooth it out reasonably assuming the pressure (or what ever it is) is displayed on the HMI as ###.# so only 0.1 resolution, if the jump in values is +/- 1.0 or more then it will still display varying data every second.
What Mas can also do is on the HMI, set the decimal places to say 1 (assuming this is accurate enough), also set the sampling rate this will slow down any change on that tag as on the HMI it is only a display & no script.
If his analogue value is changing that rapidly & by a large amount then there must be something wrong.
Ah.. I noticed the analogue is flow rate, no idea how this is controlled so it does appear to be rather bad control, perhaps he could post some information on how the flow rate is controlled, what resolution does he need etc.
 
Last edited:
It's not a problem from initial start, all the registers are initialised, the array is actually D addresses so for example a float array[0..9] is say D400- D419
so 20 addresses, these (if set in project) are retentive, if PLC is powered down then back up they keep the data, so yes for 1 second it will retain the last average then after 10 seconds will be a true average, assume the machine is stopped i.e. no pressure, then it will decay to 0, same with starting as the pressure rises so will the average, but again it will take 10 seconds to stabilise, but then again so will the actual pressure as it ramps up.
The only problem is that every second the average pressure will jump + or - rather than every scan, but the averaging process will tend to smooth it out reasonably assuming the pressure (or what ever it is) is displayed on the HMI as ###.# so only 0.1 resolution, if the jump in values is +/- 1.0 or more then it will still display varying data every second.
What Mas can also do is on the HMI, set the decimal places to say 1 (assuming this is accurate enough), also set the sampling rate this will slow down any change on that tag as on the HMI it is only a display & no script.
If his analogue value is changing that rapidly & by a large amount then there must be something wrong.
Ah.. I noticed the analogue is flow rate, no idea how this is controlled so it does appear to be rather bad control, perhaps he could post some information on how the flow rate is controlled, what resolution does he need etc.
The sensor is a differential pressure sensor.
I was given an equation to convert that dP to flow in litres/sec. The calculation is accurate and, for a given dP, the PLC-calculated flow rates match those on the engineer's spreadsheet.

When the rig is running, the flow rate doesn't vary that much, but the vertical bar is jittery and difficult for the operator to focus on one value and write it down on his checklist.

I guess ultimately, the "fix" could be done in the HMI by slowing down the display rate (although I've not seen a 'sampling rate for display' feature in the HMI, GT Designer3).

I will implement the 'average' code and report back.
Many thanks.
 
Last edited:
The average calculation is now in the code.
For the EMOV command, should D630 have the same value as D420? For some reason D630 always shows 0.

IMG_20220328_093859.jpg
 
should D630 have the same value as D420? For some reason D630 always shows 0.


See this link for that reason.


TL;DR



The [SFTLW D630 K22 K2] shifts the 20 words (10 floats) starting at D630 "up" to the 20 words starting at D632, and loads 0s into the lower (non-overlapped) two words. So that 0 in D630 is expected.



D632 <= D630 "+ K2"


20 words shifted <= "K22" - "K2"
 
See this link for that reason.


TL;DR



The [SFTLW D630 K22 K2] shifts the 20 words (10 floats) starting at D630 "up" to the 20 words starting at D632, and loads 0s into the lower (non-overlapped) two words. So that 0 in D630 is expected.



D632 <= D630 "+ K2"


20 words shifted <= "K22" - "K2"

I think I get you. Cheers Drbitboy.
So it's like once the shifting is done, D630 is "back-filled" with zeros...well, that's how I like to I think of it.
 
Extra picture added to show monitored "live" values.
D652 is the totaliser.
D654 holds the average.
I see the displayed running total is 2.09...; for the 10 floats from D632 to D650 shown in that post I get a sum of 2.02... This is not necessarily an issue, as it could be an effect of the temporal sampling of the data displayed in that window, but worth investigating perhaps.

Quick estimate/check

3 values ~0.236 (.2 + .036); 4 values ~.204 (2 + .004); 3 values ~.1666 (.2 - .1/3); 10 values total. So the excess relative to .2 is


  • 3*(.036+.004) + .004 - 3*(.1/3)
  • = 3*.040 + 0.004 - .1
  • = .120 + .04 - .1
  • = 0.024
so 10*.2 + .024 = 2.024
 

Similar Topics

how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
Replies
0
Views
84
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
Replies
0
Views
97
In this sample programming, what does U4 mean? Any assistance would be greatly appreciated.
Replies
8
Views
305
Hi, I have a project with a R04CPU, RD77GF16 and a RJ71PN92 modules. The cell is given to me to change the program since the previous integrator...
Replies
9
Views
316
Hi One of the PLC's that I maintain/update is a Mitsubishi Q-Series, probably installed about 10 years ago. At the moment, ALL the wires from...
Replies
13
Views
1,207
Back
Top Bottom