Micrologix 1400 input question

Taterfarmer

Member
Join Date
Mar 2024
Location
CA
Posts
2
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while the unit is powered on. Do I have a bad plc?

Thank you
 
If you have nothing landed on input terminal COM 3 (for that group of IN12 to IN19) and are measuring a voltage potential between any of those points and ... what is the other point of reference?

The PLC doesn't have a point of reference until you land a wire on the COM terminals and I don't think I've ever checked for the presence of voltage on a PLC input without the wiring landed on the input and its associated COM terminal, so I don't know what to expect.
 
For that matter any of the ML1400 input groups can be wired as sinking or sourcing, and if wired sourcing I would expect to see voltage on the input with nothing connected to it.

ofc, this is another way of saying the same thing as OG: check COM 3. If wired sourcing you will have a 24V wire there.
 
My apologies, com 0-3 are all tied together. The banks of other inputs don’t have voltage unless they are receiving from a sensor, this is the only bank that I have voltage coming out of the input terminals.
 
We had a failure last year on a 1400 where the inputs in a group were showing voltage when field devices were disconnected. It turned out to be an electronic failure inside the unit which was replaced under warranty.
 

Similar Topics

Hi Everybody just wondering if anybody would have a wiring diagram for the inputs for a Micrologix 1400, is it just take the 24Vdc + from the plc...
Replies
9
Views
4,831
Wired a new prox to an unused input (/14) on channel 4. I test the prox, and its light plus the indicator on the IQ16 DC Input card are tracking...
Replies
12
Views
3,333
Hello everyone.Am new in allen bradley configuration,i have a mini project to execute, i have wired my Micrologix 1400 for analog input signal of...
Replies
0
Views
1,509
Hello everyone.Am new in allen bradley configuration,i have a mini project to execute, i have wired my Micrologix 1400 for analog input signal of...
Replies
3
Views
2,615
I'm very new to PLCs and have just acquired a MicroLogix 1400 1766-L32BWA. I can see on the output terminal block two terminals (first two on the...
Replies
9
Views
3,673
Back
Top Bottom