Hello everyone, I'm having an issue trying to get a messaging instruction to work. I'm trying to get some data from a Micrologix 1400 to a L83E ControlLogix.
The MSG stays with only the "EN" bit enabled and will only occasionally enable the ER bit for a split second. The error code I'm getting is 16#0001 extended error code 16#0000_0204
My MSG instruction is setup as follows:
Message type: SLC Typed Read
Source Element: N74:0
# of elements: 10
Destination Element: L13_Int[0] this tag is data type INT[10]
Path: 2, 192.168.110.230
Communication Method: CIP
This path is the same address I use to go online with that Micrologix PLC and I have no issues going online with it. I haven't been able to find anyway to get this to work so hoping somebody has run into this before
Thanks