LS XG5000 programming software

Dr4k3

Member
Join Date
Feb 2010
Location
Sorocaba-SP
Posts
14
hello folks

I'm experiencing LS XG5000 programming software and i dont know where is the problem: with me or XG5000.
I'll explain:
I dont know how to declarate a simple timer (TON). I dont know what's going on here. Actually i'm bored and tired to try more.
People.. when i insert a TON block in my ladder logic, XG5000 says that i must to select the variables to timer but don't matter what variable i select, XG5000 returns: "incorrect variable".
What's wrong? Please someone help me... i'm already angry with this.
 
You need to manually create a tag with a data type of "TIMER". Then use this tag for your TON or TOF instruction.
 
There are several ways to create a tag. Probably the easiest is to place a TON on a rung. Type a name into the Timer field, say "Timer1". Then right on "Timer1" and click new. You will notice that the data type is "TIMER". It knows that you are creating a tag in a TON, so it automatically picks "TIMER" for you.
 

Similar Topics

Looking for help programming LS electric XGB plc to communicate with a TECO A510 vfd using modbus 485.
Replies
0
Views
677
the first question i have incremental encoder 360 pulses i want to connect in in plc ls xg5000 in high speed counter i want to know how to made it .
Replies
0
Views
2,664
Hello forum. I am very new to PLC programming and I ask your help with resetting the timer in XG5000 ST. I have two water pumps that I want...
Replies
1
Views
1,942
Hi, I hope you are well. I would like to solve the following problem: There is a LSIS PLC which needs to talk to an Omgega PID controller over...
Replies
1
Views
3,376
Hi, I am trying to set up a plc. I've never done any programming with ladder logic previously. I'm trying to set up a a program to turn a device...
Replies
7
Views
198
Back
Top Bottom