I've made a fault routine to notify operators when an IO module causes a major fault, and provided a button to manually reset the fault, but I'd like to be able to tell the operators exactly which module faulted.

(1769-L36ERM)

I've been referencing this PDF for creating the fault routine https://literature.rockwellautomation.com/idc/groups/literature/documents/pm/1756-pm014_-en-p.pdf

However, there's no information on what the "fault-specific" info DINT[8] values are. I'm thinking this might be able help me programmatically determine which module has faulted. Has anyone had experience with this?
 
Last edited:
At a previous location, I wrote a routine to display the status of each module. It used a GSV for each module. Attached is a screenshot of the GSV for an input module in the local chassis.


A screen on the HMI had a multi-state indicator for each module that looked at the destination tag.


Refer to this manual:
https://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1756-rm003_-en-p.pdf
Page 197 lists the EntryStatus values and what they mean. Page 215 talks about the fault values for the modules.

GSV_ModuleStatus.JPG
 
Last edited:
For fault routines, I typically program the following:
1. CONTROLLERDEVICE Object Status
2. MODULE Object ForceStatus and LED Status Attributes (Processor)
3. FAULTLOG object - All four attributes
4. MODULE Object for each Comm and IO Module. Alarm and Status Tag.

DI_Mod1_Diagnostic.png
 
At a previous location, I wrote a routine to display the status of each module. It used a GSV for each module. Attached is a screenshot of the GSV for an input module in the local chassis.


A screen on the HMI had a multi-state indicator for each module that looked at the destination tag.


Refer to this manual:
https://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1756-rm003_-en-p.pdf
Page 197 lists the EntryStatus values and what they mean. Page 215 talks about the fault values for the modules.
I ended up doing basically this. One GSV for each of 15 modules.

I just want to log which module faulted, not necessarily why (at this moment in time).
So, I compiled the fault codes into an array and looped through to check for error codes (NEQ 0). There's a parallel array of static STRING tags that get appended (CONCAT) to the base alarm string.
 
I typically monitor the I/O indicator on the controller as my starting point. When it is flashing green I use that to call a subroutine where I have my GSVs for the local I/O and communication modules. That way I'm not triggering all those GSVs when there isn't a problem.

If a communication module is the cause, then I use that to call a subroutine with GSVs to check all the "child" remote communication modules to see which one of those have an issue. When I find out which remote chassis has the issue then I use that to trigger GSVs to the modules in that remote chassis.

OG
 
I typically monitor the I/O indicator on the controller as my starting point. When it is flashing green I use that to call a subroutine where I have my GSVs for the local I/O and communication modules. That way I'm not triggering all those GSVs when there isn't a problem.

If a communication module is the cause, then I use that to call a subroutine with GSVs to check all the "child" remote communication modules to see which one of those have an issue. When I find out which remote chassis has the issue then I use that to trigger GSVs to the modules in that remote chassis.

OG
Yes, I'm only calling the GSVs in the fault routine. After processing all the GSVs and creating my alarm description string I auto-reset the module. The bit that triggers the alarm for the operator stays on so they know which modules failed.
 
@AMarks95:
Please send me a PM with your email I got an example for module testing and identify which one is the bad.
It is written in V20 because that was the version of the customer, you can changed it to any other version.
 
I typically monitor the I/O indicator on the controller as my starting point. When it is flashing green I use that to call a subroutine where I have my GSVs for the local I/O and communication modules. That way I'm not triggering all those GSVs when there isn't a problem.

If a communication module is the cause, then I use that to call a subroutine with GSVs to check all the "child" remote communication modules to see which one of those have an issue. When I find out which remote chassis has the issue then I use that to trigger GSVs to the modules in that remote chassis.

OG

OG

Is that program something you could share a sample of? I never knew that functionality was there and would love to check it out in depth.
 
There's an AOI from Rockwell called Module_Sts that provides this and other details (with faceplates too). You point the module to it and it retrieves data.
 

Similar Topics

​Hello everyone, I triyng to link a Power Module eMB-60R from Robot Adept Viper s650 to CompactLogix, version 19.11 I followed exactly the...
Replies
9
Views
2,663
I have a subroutine that gets called to copy a UDT In an array to a tag. This subroutine will be called around once per minute and has been...
Replies
4
Views
2,123
Anybody know if there is a registry entry that can be changed/added for Logix/Studio 5000 that will change the default data type for an analog...
Replies
14
Views
6,383
Hello, It's seems that i can't make an upload from the safety PLC. Im using a L61S PLC. I'm able to start the upload, but when its half way...
Replies
5
Views
2,280
I'm fairly new to working with servo control. My training is coming, but I have a customer that needs help right now, so I'm trying to read/work...
Replies
5
Views
2,914
Back
Top Bottom