Large 480V heaters vs motors

Rson

Member
Join Date
Jun 2017
Location
Michigan
Posts
520
I know with larger motors you do not want them to start with a contactor above 30HP or so because they will 'sag' the power in the plant and the inrush current can be insane. We typically put anything at or above 30HP on a VFD or Soft Start unit.

Is there any such worry about a large 480V heating element? They are resistive loads, so there should be no worry about inrush. Is there a certain point you would want to switch to an SCR controller even if you want 100% of the heat all the time?

A 60kW heater, for example, would pull just over 72A at 480VAC. Is a simple contactor still a suitable way to turn it on and off, or is there merit in controlling this with an SCR instead?
 
Don't really think it matters, although contactors being mechanical SCR's can be more reliable with the exception of shorts causing damage. If these are not being switched at any great frequency then contactors are a better idea, an SCR can go short especially on a short i.e. somebody drops a spanner across the heater, so providing it is fused correctly either is good.
 
In my mind, the only reason an SCR would be preferred would be if the switching frequency was high. If rapid and frequent on/off cycles are employed with mechanical contactors they would beat themselves to death in short order.

The downside to using SCRs for a sustained resistive load is the heat that must be dissipated. The SCR should be fitted with a heat sink, and that heat would go into the panel. You can use a bypass contactor that pulls in after the SCR has switched on, but then I see little point in the SCR in the first place.
 
I almost always use mechanical contactors unless I want to vary the power to the heater. EDIT: for high amp I use mechanical mercury coontactors.


Because of the possibility of frequent cycling I always put a ant-chatter control.



When the input comes on it stays on for at least 10 seconds and when it turns off it stays off for at least 10 seconds.


I also do the same for solenoid valves to fill or empty a tank in case the float is bouncing on an unstable liquid surface.
 

Similar Topics

Hello, I'm digging all over the internet to find a solution for this but haven't come up with anything yet. We have 3 nearly identical machines...
Replies
2
Views
968
Hi All, On my site, the standard template for storing recipes in the PLC is to create a tag called PartRecipe which is an 2D array - for example...
Replies
4
Views
1,475
We have a panel with a 125HP VFD. We need to run #3/0 wire from the disconnect to the VFD & line reactor. The normal stuff is hard to bend and...
Replies
11
Views
2,803
Working on an upgrade project, going to replace an L63 revision 17 with an L74 revision 30. In newer L74, MSGs with large tags as source/target...
Replies
0
Views
774
Hi everybody, I was given a large excel file with 1,000 rows and 7 columns that are arranged in a way to show the total volume of a cylinder at...
Replies
13
Views
2,649
Back
Top Bottom