L23E Compactlogix Noisy Analog Input

desertsurf520

Lifetime Supporting Member
Join Date
Jan 2018
Location
Tucson, Az
Posts
61
I had some recent issues with the analog inputs on an L23E. At first, I did not wire the analog com back to 24 neg and that was a lot of it. However, I have since corrected the wiring issue and the analog counts are much more stable.

Still, even with everything wired correctly, the counts seem to jump a small percent but they still jump and this is at multiple sites. I monitor the mA and VDC (250 ohm resistor in the card) and both are steady and stable while the counts like to jump.

I believe this is a power or grounding issue as the panels are plastic boxes and the electrical was not installed very high quality. A couple of the sites have the correct electrical system and some are more mickey mouse style. I don't have a ground test set but I am trying to reason with the customer.

The noise is on the PLC side not from the instrument itself.

Has anyone else had issues with this processor or similar having counts jump up and down or somewhat unsteady.

Thanks
 
I think it was around 1000 or 1500.

The wire is potted in the level transmitter but it did not come twisted shielded. It is twisted only. However, when measuring mA and VDC it is very stable even to the hundreths or thousands
 
It is not right now but the engineer wants to try that, too.

I don't think the whole AC power system is grounded very well plus its in a poly panel and the backplate is aluminum and is not properly grounded.
 
What is the complete part number of the L23E?

What is the part number of your analog input module?

I have a recollection of those packaged controllers using the DIN rail mount as a means of grounding. I would definitely ground the backplate and ensure that the DIN rail and ground terminal on the controller are properly grounded.
 
I think it was around 1000 or 1500.

The wire is potted in the level transmitter but it did not come twisted shielded. It is twisted only. However, when measuring mA and VDC it is very stable even to the hundreths or thousands
is that an answer to the query "how many bits of noise?" so noise magnitude is 1-1.5k raw counts? And that is out of 16384 or 32k or 64k?
 
Just across the channels input terminals.

As ask above what is the catalog number of your analog module?
 
L23E QBFC1B

I tried connecting all I+ to common but that did not help.

It's jumping from 28416 to 28500. It seems to just bounce back and forth.

Re-ran cable and grounded the shield at one end.
 
According to the documentation I can find, the input data for the embedded analog inputs is:

Bits 0-6: not used
Bits 7-14: 8-bit analog input value
Bit 15: sign bit (always positive)

28416 in binary: 110111100000000
28500 in binary: 110111101010100
...so what you're seeing is the smallest possible change that the analog input can represent. Though I'm not sure why some of the "not used" bits are also turning on/off, unless "28500" was just a rough figure and it's actually 28480?

Is there logic in place to extract those 8-bits into a standalone integer? And is the variation you're seeing before or after that happens?
 

Similar Topics

Hello everyone, Anyone know how to factory reset CompactLogix L23E?
Replies
1
Views
1,749
Hello,i need your help. I cant connect to a CompactLogix L23E, I tried via Ethernet and Serial too. The PLC has a IP configured, I have ping it...
Replies
3
Views
1,496
Hello everyone, we want to change IP address for used compactlogix L23E-QB1B controller ,it assigned a IP address before, but this IP address is...
Replies
14
Views
2,813
I am newcomer here, I bought a AB compactlogix l23e embedded i/o plc(used one) a few days ago. I made a stupid decision i think that I downgrade...
Replies
5
Views
1,667
I am trying to test a scanner application where I am converting RS232 to Ethernet IP, and then reading the results at an A-B compactlogix L23E...
Replies
5
Views
3,393
Back
Top Bottom