unsaint32
Member
I am an automation technician working on Kinetix 300 drives with Motionview Onboard.
We have two different setups;
- Controllogix 5000 to the Kinetix 300
- Micrologix 1400 to the Kinetix 300.
I have to disable the drive in order to change the drive mode from indexing to autotuning.
With the Controllogix setup, I force off a PLC output to cut off 24V signal to the Kinetix 300's terminal 29. Then I can see in the MotionView Onboard that the drive is switched from "Enabled" to "Disabled."
With the Microllogix setup, however, when I force off the PLC output to the drive's terminal 29, the drive faults.
As you can see in the picture, with the Controllogix setup, I have additional "enable" data being sent. But when I force that one off, that didn't make any difference. I still can force off the Controllogix PLC output and successfully "disable" the drive without getting the fault.
Likewise, in the Micrologix setup, I force ON the L11:0/7, then force off the PLC output, I still get the fault.
How can I change the drive between disabled and enabled without causing fault? Thanks. d
We have two different setups;
- Controllogix 5000 to the Kinetix 300
- Micrologix 1400 to the Kinetix 300.
I have to disable the drive in order to change the drive mode from indexing to autotuning.
With the Controllogix setup, I force off a PLC output to cut off 24V signal to the Kinetix 300's terminal 29. Then I can see in the MotionView Onboard that the drive is switched from "Enabled" to "Disabled."
With the Microllogix setup, however, when I force off the PLC output to the drive's terminal 29, the drive faults.
As you can see in the picture, with the Controllogix setup, I have additional "enable" data being sent. But when I force that one off, that didn't make any difference. I still can force off the Controllogix PLC output and successfully "disable" the drive without getting the fault.
Likewise, in the Micrologix setup, I force ON the L11:0/7, then force off the PLC output, I still get the fault.
How can I change the drive between disabled and enabled without causing fault? Thanks. d