Issue with AOPs and EDSs

nievesdelimon

Member
Join Date
Mar 2018
Location
Queretaro
Posts
39
I posted a couple months ago about something similar, but it happened again and now I have more information.


On the project's I/O tree there's a 1734-AENTR/C I/O point showing up as a yellow questionmark instead of its icon and <unknown> where its name should be. The device's revision is 7.011.


I downloaded all the EDS and AOP files I could find on Rockwell's websits, installed them and nothing changed, however, a coworker did the same and it did work for her, the device appears as it should, icon, name and properties can now be accessed from her computer.



The problem appears to be on my side, but I need help identifying and fixing it.



I would appreciate any help from you guys.
 
Rockwell devices support uploading EDS file to RSLinx. If you are seeong the yellow question mark ir is because the EDS you installed does not correspond to the firmware or maybe even hardware version of the remote IO device. This will be fixed by uploading the EDS from the device itself.
 
You mean your coworker is using a different Windows PC?
The EDS catalogue that RSLinx uses is not related to the the EDS files used in the Logix project. You need to update the catalogue of USD files in RSLinx by uploading the EDS file from the device to eliminate the yellow question mark.
 
Yes.


I can see the devices on RSLinx -their icons instead of yellow question marks-, the problem is only on Logix Designer. Even after uploading the EDS files from the devices the issue persists.
 
Last edited:

Similar Topics

Hello everybody, I have Kinetix 5500 (2198-H040-ERS). I'm having issue with this drive. (I believe it's the drive/Kinetix and need confirmation)...
Replies
0
Views
47
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
Replies
4
Views
168
Hello all. I am trying to communicate to an ASi gateway from my CpLX (L16ER). I am able to ping the gateway and it replies. I configured the...
Replies
5
Views
138
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
18
Views
388
I want to communicate my Q series PLC with Factory IO using GX works 2 software, I want to use modbus as server and the ips are as follows plc...
Replies
0
Views
88
Back
Top Bottom