Again, nice idea and I appreciate it, but drilling through the vessel is a no-no.
I thought that might be the case.
So the WIKA uses a wireless signal?
Again, nice idea and I appreciate it, but drilling through the vessel is a no-no.
No, it's not wireless. The cable feeds through a gland of a specially designed "porthole" and is routed to the PLC. The breather tube stays inside the vessel though.I thought that might be the case.
So the WIKA uses a wireless signal?
No, it's not wireless. The cable feeds through a gland of a specially designed "porthole" and is routed to the PLC. The breather tube stays inside the vessel though.
Use a capacitive level probe.
How does the drain to the pump exit the vessel? Would it be possible to run a small line into that? Or add a pressure instrument to the drain just outside the vessel?
Probably the best solution is to get Erwin SICK representative in to discuss the requirements, I would have thought an analogue rod probe type if it could be mounted would be the best, not used them on a vacuum but do not see any reason why it could not be used.
The probes I was thinking about is a rod type do not need breathers or alike it is just a rod like a level probe but instead of just detecting level it will give out an analogue level based on how much of the probe is covered, vacuum should not affect it but would need to be confirmed.
Not sure I understand the question.
I've sketched a poor picture of the pump relative to the vessel. Pump sits on the floor, not partially buried like in the sketch. There's a drain cover plate, above which the level sensor sits.
The idea was to run a pressure tap through the side of the drain and up through the drain into the vessel.
But we may be looking at this wrong. If there is a vacuum of 20Torr above the liquid level in the sump, then that adds 37.2cm to the target minimum level used when there is no vacuum. So if the drain pump comes on at 50cm, and stops when the level drops to 10cm whenever the pressure above the liquid is atmospheric (0Torr; no vacuum) to avoid cavitation, then when there is 20Torr of vacuum, the pump should come on at 50cm* but go off at 47.2cm (10cm + 37.2cm).
What we really want to do is stop the pump when its suction (intake) gauge** pressure goes below some point, and we don't need the level to measure that pressure, and presence or abscence of a vacuum does not change what that pressure is. Then, when the pump is off, the gauge pressure at the suction (with no flow) at which to turn the pump back on, which pressure corresponds to a level of 50cm, can be calculated as long as the vacuum above the level is known.
So we don't need a level measurement at all; all that is needed is the gauge (atmosphere-relative) pressure measured at the pump suction, and the vacuum (again atmosphere-relative) measured above the liquid inside the vessel.
* I assume the 50cm level specification is geometric i.e. the level gets close to some piece of hardware in the vessel that should not be submerged in the water.
** "gauge pressure" means "relative to atmospheric."
You've lost me in the science there...