Hello Guys, I'm working on Honeywell HC900. I am using the PID block. I have attached the Switch and loop block to it as well. I have attached a Screenshot for reference.

I'm unable to figure out how the value of the manual output will be entered in this block, Kindly help me in this regard.

And what is the difference between remote and local set points?

PID Logic.PNG
 
right click on the block and go to help. HC900 help on its function blocks is great.
Remote setpoint is from somewhere else (like a SPP block).
Local Setpoint is set in the function block, or can be accessed from a "Write Variable" block.
 
You do know that you can tag name the variables.


Is there some reason your thermocouple input is not the input (top of the PID FB) where VAR131 is shown?
 

Similar Topics

Hey Guys, I am getting random rack/slot errors. I go to download and everything is ok but then it has a error. For example - Yesterday everything...
Replies
1
Views
369
Does anyone have experience with setting up a HC900 to a prosoft card? Using this to communicate with an Allen Bradley plc
Replies
1
Views
699
Greetings! I'm trying to connect HC900 to Kepserver in Plant via HC900 ethernet driver provided by Kepserver. I put the IP address and most of...
Replies
0
Views
1,119
Hello All, I have problem with Honeywell HC900 C50 CPU, the problem is my all local IOs cards not communicate with CPU. I attached a picture of...
Replies
2
Views
1,661
Dear Buddies, I'm new to Honeywell product, So I start with some basic question: I downloaded the demo version of designer software from...
Replies
4
Views
2,149
Back
Top Bottom