Possible dumb question here, but how does running a motor through a gearbox effect a VFDs ability to limit the torque on the driven load? My gut says the VFD torque limit would be multiplied by the gear ratio, but my gut is often wrong so I figured I would ask here.

Also, if the VFD has a torque limit range of 0-350% (Weg CFW500) how would I go about relating that percentage to desired lb-ft?

10HP motor / 1800RPM
10:1 gearbox w/ 96% efficiency
 
how does running a motor through a gearbox effect a VFDs ability to limit the torque on the driven load
Not at all. The VFD limits the torque output of the motor. That torque, applied to the gearbox input shaft is multiplied by the gearbox's reduction ratio at the output shaft.
The formula for converting HP to torque is:
Torque = (HP * 5252) / RPM
 
Not at all. The VFD limits the torque output of the motor. That torque, applied to the gearbox input shaft is multiplied by the gearbox's reduction ratio at the output shaft.
The formula for converting HP to torque is:
Torque = (HP * 5252) / RPM

Thanks! Looks like my gut was right on this one.
 

Similar Topics

Good Afternoon , I have a 5 Hp SEW Eurodrive motor S.O.# 87.8070060501.0002.22.90 KA67/T motor. I'm trying to find the Terminal Block that...
Replies
6
Views
2,074
From an existing configuration I know the default set acceleration of the motor in rev/sec². Attached to the motor is a gearbox with ratio 1/10...
Replies
9
Views
2,507
Good Morning , We are going to need to change a gearbox that as a MPL-B540K-MJ24AA connected to it. The gearbox is 19.5 : 1. The problem is...
Replies
11
Views
4,394
We have some Siemens servomotors that are overheating. If we look at the load, current and speed, there is no reason at all for overheating. Also...
Replies
5
Views
2,627
I am using a servo motor to make my own rotary indexing table which will have 6 nests. My servo motor has 65536 counts per revolution. I am...
Replies
5
Views
3,137
Back
Top Bottom