Hi all
Currently facing this question which contribute a lot white hair.
I am setting a redundant system with 3 display clients.
I am using direct reference alarm and configure primary server as alarm server.
I facing problem where the clients cannot view the alarm when the primary server is disconnected from network and the secondary server take over to become active.
I found that in the manual that FTView does not support redundant in alarm and events.
Is there any solution for this as alarm is very important in this project.
Hope someone can help me here. Thanks alot.