I'm trying to wire a Endress+Hauser PMP71 Pressure Transmitter to a Schneider Electric TM3AI2H Analog Input Module. The Pressure Transmitter is powered by the 4-20mA loop. If I wire 24+/24- to the Transmitter it powers up as expected but when wiring to the Module it does not power up. Seems pretty basic but not working as anticipated. Sending 24+ to the E+H + Terminal. The E+H - Terminal is terminated on the Analog Input Module Terminal I0+. The 24- is terminated on the Analog Input Module Terminal IO-.

E+H PRESSURE TRANSMITTER WIRING.png TM3AI2H ANALOG MODULE.png
 
It looks like it is loop powered, so connect 24V to the +ve terminal of the E&H connect the -Ve terminal of the E&H to IO+ of the card & 0V to the card IO-.
 
It looks like it is loop powered, so connect 24V to the +ve terminal of the E&H connect the -Ve terminal of the E&H to IO+ of the card & 0V to the card IO-.

This is exactly what I was thinking and wired it up as. The Pressure Transmitter doesn't power up as expected however. Per E+H I hooked up 24+ and 24- to the Pressure Transmitter to test powering up and it does power up as expected, but not when connected in the 4-20mA loop.
 
As I read it, you wired the loop properly, but have you powered the AI card with 24Vdc on the 24V and 0V terminals?
 
Is the card a MA and Voltage input type card? If so, have you correctly configured it for MA input? Some cards have dipswitches or jumpers, others are software configurable.
 
Software configurable and that was the issue it seems. I'm new to the Schneider Controllers. Connected to a Unitronics unit and worked without issues. I had someone do the base program since I was new to it and I went in behind and cleaned it up, added to it and made it more to where I could troubleshoot easier if needed. They set up and scaled the 4-20mA in the ladder but they left it Not Active on the AI Module configuration. I updated to 4-20mA and it seems to be working. Appreciate everyone's assistance
 

Similar Topics

Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
265
I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
Replies
4
Views
169
Hi All, Just wondering what the best/most accepted way to measure tank level off pressure transmitter. Pressure transmitter is located in line...
Replies
6
Views
1,936
Hi folks, I am having a hell of a time getting an E+H PMP23 scaled correctly in a CompactLogix PLC. I have tried all sorts of data manipulation...
Replies
19
Views
7,010
Hello Everyone , Hope you all are well and safe sound! I'm looking solution for the pressure transmitter which are installed in Blender or Lpg/...
Replies
8
Views
2,885
Back
Top Bottom