@drbitboy rung 0 stop would be a XIC
Depends on how the physical stop button is wired.

In the US it's typical to use NC contacts on a stop button. If that is the case when you're not pressing the stop button the XIC addressed to that device evaluates as true, so rung 0 should be an XIC. If the stop button is wired using a NO contact, then the XIO instruction is correct.
 
Last edited:
Depends on how the physical stop button is wired.

Agreed.
NC stop buttons is the approach we use too. Although it's common to see machines from overseas arrive with N/O contacts on start and stop buttons.

My comment was more so just to have rungs 0 and 1 on @drbitboys examples equivalent.
 
My comment was more so just to have rungs 0 and 1 on @drbitboys examples equivalent.




Wait. I still don't have it right? Oh dear ... :confused:


I used [XIO STOP(I:0.0/0)] initially so I could do everything on the MicroLogix 1100 without playing with wires.


I tested it. Or so I thought. hahahaha.
 
Last edited:
guys. I thought for first step. Is it correct whren i push start button after 20 sec lamp it opened but i didn't continue second step.

Adsız.png
 
guys. I thought for first step. Is it correct whren i push start button after 20 sec lamp it opened but i didn't continue second step.


Excellent! Well done: the light [O:0/0] turns on 20s after the input [I:0/0] becomes 1. This is a classic TON (Timer-driver ON-delay) circuit.



Also, the [OTL O:0/0] latches the light ON (assigns 1 to O:0/0), so when the timer is reset and [T4:0/DN] become 0, the light will stay on. That can be good too*, but at some point we will want the light to turn off as well, even though T4:0/DN may be 1. Also, if the input switch is turned off ([I:0/0] becomes 0) after 20s, then the timer will reset and [T4:0/DN] will become 0, but the light will say latched on. So there may be some more logic (instructions) added to Rung 0001 later to disable the latch [OTL] on every scan, and there will need to be a way for the light to turn off that looks at the input switch, but this is good for now.



The next step is to reset the timer 20s after it starts timing, so it can start the next 20s cycle.

  • What is the trigger to do that reset?
    • Hints: what bit becomes 1 at 20s after the timer starts? You did something similar on Rung 0004 of Post #7

* The light could also be turned on, and kept on, with an [OTE O:0/0] fed by rungs that contain additional logic, instead of the OTL triggered by [T4:0/DN]. Sometimes an OTL is not preferred: for example if the PLC lost power, then the light would be on ([O:0/0] would be 1) when the power came back, and that might not be what was desired. But leave it as a latch for now.
 
Last edited:
Did you mean that for the second steps, but how is it going to turn off the latch in the transition to the last step?

Adsız.png
 
Did you mean that for the second steps, but how is it going to turn off the latch in the transition to the last step?




Perfect!


Consider that the T4:0/DN Bit will behave like this:
Code:
Time ===>


T4:0/DN=1:            -           -           -
                     | |         | |         | |
T4:0/DN=0:  ---------   ---------   ---------   ---- ...
So the T4:0/DN bit will be 1 for one scan every 20s; another way to say that is that T4:0/DN will have a rising edge every 20s.


Can you find a way to count those rising edges, and then use that count to inhibit the the timer, and turn off the light, after the third rising edge?


Hint: you will have to edit one, or more, of the existing rungs in such a way that it changes their behavior at the third 20s event, but does not change their behavior at the first [T4:0/DN]=0 event.
 
Last edited:
Also note that, with the current program, if the input switch is turned off between 20s and 60s, then the light will remain ON, because [O:0/0] was latched to 1.


So you will need some logic to turn off the light if [I:0/0] becomes 0. The timer will reset because the [I:0/0] controls the timer input rung, so you will not need to either do anything to the timer rung or add another reset.
 
Consider that the T4:0/DN Bit will behave like this:
Code:
Time ===>


T4:0/DN=1:            -           -           -
                     | |         | |         | |
T4:0/DN=0:  ---------   ---------   ---------   ---- ...
So the T4:0/DN bit will be 1 for one scan every 20s; another way to say that is that T4:0/DN will have a rising edge every 20s




And another way to say that is that T4:0/DN will have a false-to-true transition, although it would be better to say it will have a zero-to-one transition, every 20s.


I add this because the problem statement seems to come from a book's chapter 8 "Programming Counters" cf. https://sanamrao123.files.wordpress.com/2015/04/ch-8.pdf, and that phrase "false-to-true" is used fifteen times in that chapter.
 
Last edited:

Similar Topics

The ProSim-II Silo Simulation From the Simulations Menu at the top of the screen, Select the Silo Simulation Exercise...
Replies
9
Views
5,907
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
104
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
Replies
4
Views
174
I have an old PLC (circa 2007) consisting of Telemecanique/Modicon/Schneider Electric devices. The system has developed errors and unfortunately...
Replies
2
Views
254
Hello, I am trying to figure out how to create / write / delete a .csv file on the SD card of an Allen Bradley PLC. There is a sample project...
Replies
1
Views
1,440
Back
Top Bottom