Good day,

I got a concern regarding the Redundancy setup. The problem is when communications get interrupted between the Primary PLC and the remote I/O rack. The outputs of a Digital Output module get triggered unintentionally shutting down critical processes in the plant. The PLC we're using is 1756-L73 with 1756-EN2T Ethernet module.

I'm wondering whether the PLC being connected to a POE network could be a problem (see attached system architecture).

Could there be a technique to make redundancy configuration fail safe? Or I probably need a comms failure signal to Secondary and remote I/O rack?! Thank you very much.

Sincerely,
AndreiK

CtlLgx_Redundancy_Config.jpg
 
Thanks for the concise diagram !

Are the outputs on the remote chassis transitioning from OFF to ON, or from ON to OFF ?

Are they remaining in that state, or transitioning for a short period of time ?

Does the Secondary take over the I/O connection correctly and run the system, or does the switchover fail ?

Ethernet networks for Redundant ControlLogix need to be set up carefully. Have you talked to Rockwell about this POE switch ?

What you're describing sounds like it might be related to a bug in the 1756-EN2T firmware from a couple of years ago (Link), but that existed when a connection was dropped and re-created, not when a Redundancy switchover occurred.
 
Good day mr. Ken,

Outputs on the remote chassis transition from OFF to ON.

Transitioning occurs for a short period of time.

I tested the switchover before and was working just fine. When the comms failure to the remote chassis occurred there was no switchover. The secondary got disqualified from the Primary at the same time.

I haven't talked to Rockwell about the POE switch.

That seems to be the case! It wasn't a switchover but a communications drop.

Thank you very much!


Thanks for the concise diagram !

Are the outputs on the remote chassis transitioning from OFF to ON, or from ON to OFF ?

Are they remaining in that state, or transitioning for a short period of time ?

Does the Secondary take over the I/O connection correctly and run the system, or does the switchover fail ?

Ethernet networks for Redundant ControlLogix need to be set up carefully. Have you talked to Rockwell about this POE switch ?

What you're describing sounds like it might be related to a bug in the 1756-EN2T firmware from a couple of years ago (Link), but that existed when a connection was dropped and re-created, not when a Redundancy switchover occurred.
 

Similar Topics

Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
86
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
198
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
80
Hi Guys, Is it okay to have Redundancy ControlLogix Processor IP address set to DHCP? I had Static IP address on it but removed it via RSLinx...
Replies
3
Views
241
Hi Guys, For a Redundant Controllogix L81E with EN2TR, on a Device Level Ring; does the Controller also require IP address assigned?
Replies
2
Views
172
Back
Top Bottom