I'm having an issue trying to backup a ControlNet network. Within RSLogix5000, when I click on Module Properties of the 1756-CNB (Rev 5.001), the button to launch RSNetworx creates an error box:
"Failed to create new controller device in ControlNet project file. Verify EDS file exists: 0001000e005c1400.eds" (Yes it exists)
I've had to find EDS files for the 1756-L71 (Rev 20.18) on PCDC. The EDS Hardware Installation wizard keeps skipping over a huge section of EDS files for :
(0001000E005C1400.EDS)
"The following warning occurred in the [File] section of the EDS File: The CreateDate entry is not a valid date or format"
"The following warning occurred in the [Connection Manager] section of the EDS file: The O->T Real time format of the 'Connection parameters' field in the entry 'Connection1' must be 'heartbeat' when the 'application type' is input only or listen only."
Upon checking PCDC, our version of RSLinx (4.2) doesn't have a compatibility check mark but the box is blank. So it's not incompatible, but I can't get past these errors. Any ideas? Rockwell's Engage forum is mute at this point.
"Failed to create new controller device in ControlNet project file. Verify EDS file exists: 0001000e005c1400.eds" (Yes it exists)
I've had to find EDS files for the 1756-L71 (Rev 20.18) on PCDC. The EDS Hardware Installation wizard keeps skipping over a huge section of EDS files for :
(0001000E005C1400.EDS)
"The following warning occurred in the [File] section of the EDS File: The CreateDate entry is not a valid date or format"
"The following warning occurred in the [Connection Manager] section of the EDS file: The O->T Real time format of the 'Connection parameters' field in the entry 'Connection1' must be 'heartbeat' when the 'application type' is input only or listen only."
Upon checking PCDC, our version of RSLinx (4.2) doesn't have a compatibility check mark but the box is blank. So it's not incompatible, but I can't get past these errors. Any ideas? Rockwell's Engage forum is mute at this point.