Good Morning ,


We had our 2nd episode in 4 weeks with a 1756-L62 processor causing a backplane communication issue , that caused us to lose communication to our Sercos , input and output modules. We changed the Power Supply , Backplane ,etc.


Even powering the rack down and back up , never restored the communication. The CPU never showed a fault.


Been speaking with Rockwell and they sent me Technical Note ID 41204 , about a noise issue in a number of 1756 modules manufactured from September 2006 thru June 2007.In the technical note they refered to a ASIC component . If it had ATMEL stamped on the component it was a possible module that had that potential to fail due to noise issues.


When it fails , the following slots show the following....


Power Supply - Good
Slot 0 - 1756-L61 Good
Slot 1 - 1756-ENBT Good
Slot 2 - 1756-M16SE Faulted ( This does say ATMEL but
not the correct number )
Slot 3 - 1756-IB32 Faulted
Slot 4 - 1756-OB32 Faulted
Slot 5 - 1756-IB16 Faulted
Slot 6 - 1756-OF 8 Faulted
Slot 7 - 1756-OF 8 Faulted
Slot 8 - 1756-IR6I Faulted
RS Linx only sees the Processor and 1756-ENBT module.


Have you guys ever seen this before ?


Thanks so much for your help.
 
There was another thread a couple of weeks ago with similar symptoms; 1756-L6x, SERCOS module, all other modules faulted. I checked Cydog's post history and it doesn't appear to be him, so I guess it's just coincidence.

"Why do I have to keep troubleshooting" is a bit of a rhetorical question. You need to keep troubleshooting because you haven't found the problem, haven't fixed the problem, or there is more than one problem.

I sympathize, I really do. But you've got to use basic process of elimination.

If the CPU isn't the problem, and the backplane isn't the problem, and this has run for a decade without exhibiting the problem... then it's probably the 1756 SERCOS module.

The SERCOS modules, like CPUs and network modules, have a more sophisticated backplane interface than the I/O modules do. If their backplane chip malfunctions it can prevent modules other than itself from communicating with the CPU or Ethernet.
 

Similar Topics

what keeps setting my local PLC time 8 hours back? even when I hit the "set time to workstation", it immediately gets overwritten.:confused:
Replies
6
Views
5,583
I have a Allen Bradley Control Logix 1756-L62, and we have an applicattion that takes the time from the PLC. Since a couple of weeks, we have the...
Replies
6
Views
3,787
We have a project where we have the 1756-L82Es in redundancy with Remote IO Backplant via EN2TRs. Everything works and is redundant but we can...
Replies
2
Views
396
Hi there! I posted few days ago about a fault i had with my motion. I did some cable check and replacement and it didnt solve my problem yet but...
Replies
0
Views
390
Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
Replies
6
Views
1,116
Back
Top Bottom