Hi,
i have been given the task of measurring temperatues of a certain cooking chamber in my factory...they have a plc omron cqm1h-cpu21.
My boss said to connect a pt100 which is thermo sensor....
How to do it?
Plzz help me...
Thanks
 
Hi,
i have been given the task of measurring temperatues of a certain cooking chamber in my factory...they have a plc omron cqm1h-cpu21.
My boss said to connect a pt100 which is thermo sensor....
How to do it?
Plzz help me...
Thanks

It the CQM1H already has an Analog Input Card with a spare Channel, probably the easiest would be to install a PT100 to 4-20 mA Transmitter.

Stu.....
 
sthompson's suggestion is a good one, if you have analog.

If not, there is not a simple temperature sensor input module for the CQM1/CQM1H product. You could use a temperature controller module with PT100 sensor input, part number CQM1-TC101.

This module will require at least 1 input and 1 output word allocation.

Hope this will help.
 

Similar Topics

Hi I want to connect one PT100 to two measuring devices. Is this possible? Currently PT100 goes to a 4-20mA converter. From there we want to read...
Replies
3
Views
2,391
Hi, i have 1 problem which is i wana monitoring the temperature which detected by PT100 to NAIS PLC FP2. how do i direct connect direct from PT100...
Replies
3
Views
2,992
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
Replies
3
Views
107
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
Replies
0
Views
60
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
84
Back
Top Bottom