We have an old system controlled by a siemens plc s5 with order no. 6es5 102-8ma02 we want use for this system operating panel siemens op25 but so far cant I want have information about how to communicate bettwin plc s5 and op25. please help me</SPAN>
 
Dear M. hajihasani,
Op25 Have port TTY. which is directly communicate over programming port of S5 PLC. You need ProTool For Op25 programming and OP25 to PLC cable.
Regards,
 
dear zahid
tanx for your reply.but i need to know how i can write a program or data block in s5 plc for this communication, whether this communication need to a specially db or fb .
best regard
m.hajihasani
 

Similar Topics

We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
95
I have a slc500 plc 1747-L30A. Using a communication cable 1747-PIC cable box combination. Running a version of software from DOS on a Windows 3.1...
Replies
8
Views
148
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
18
Views
408
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
239
Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
0
Views
51
Back
Top Bottom