Hi,

I'm setting up a new cell with a Fanuc R30iB and Compact Guardlogix 5380 PLC.

I have gone through my robot setup as usual, but have not been able to get communication between the robot and PLC. We have setup the same cell multiple times before and have only had this issue on this cell.

Within my PLC the robot is showing module fault (Code16#080a) Safety Parameter Error: Invalid CPCRC

I have not found helpful resources online and was wondering if anyone would be able to assist or explain this issue.

Thank you
 
From what little I can find, it appears maybe that you are attempting do a safety connection and the safety signatures don't match?
 
It ended up being solved by go offline and downloading again to the PLC instead of going online. There was a thread in the Rockwell Knowledgebase that provided troubleshooting for this issue.

Thank you for your help though Steve
 

Similar Topics

I am facing problem of my Plc going to fault mode intermittently. on my AB Compactlogix PLC Fault coming is code16#009 module configuration...
Replies
1
Views
2,893
Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
Replies
0
Views
75
After some interesting conversation regarding the safety of emergency stops, I saw some posts talking about the safety standard conversation...
Replies
26
Views
960
Hi, I am using AB 5069-L306ERS2 CPU. My system should achieve SIL-2. I have safety door switches connected to AB 5069-IB8S module, and I want to...
Replies
1
Views
130
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
120
Back
Top Bottom