I don't think you can do it with that hardware. A PLC-5 may have a channel configured as a RIO adapter in order to share information with a scanner from a different PLC.

For two SLCs, you could use the 1747-SN in one of them and the 1747-DCM in the other. We have a PLC-5 that communicates over blue hose to 4 SLCs each with a DCM module.
 
I second Paul SN to DCM.
what processors do you have? You could use comms. to make it work. That is my prefered method to make systems talk
 
You're both correct on the 1747-SN to 1747-DCM being the way to use RIO to interlock two SLC-500 controllers. There's a Knowledgebase document, number 29223, that describes this connection in detail.

You could also do this using ControlNet with 1747-SCNR modules, or using DeviceNet with 1747-SDN modules, but the most common method to "interlock" SLC controllers over a network is ordinary MSG instructions.
 
ken do you setup the SDN as 1 master ans the others as slaves? Isn't there a way to explicit messaging in Dnet? or is that just one of the things I had a dream about?
 
The project will contain a PLC5 communicating to an SLC rack and an Motoman robot. The PLC5 will be the master. Is the DCM card still they way to go?
 
Which controller do you have for the Motoman? Do you have a MARIO card (Motoman Allen bradley Remote I/O)? What communication to you plan on using to and from the Robot? That will make a world of difference.
If you have a DeviceNet anybus card in the Robot then why go RIO? That is just an example of what you may have.

If you are going to talk RIO and have the PLC5 as the master then yes the DCM is the way to go.

What do you want to be the master? PLC5 or SLC
 

Similar Topics

Does anyone have information or documentation regarding the protocol used in Rockwell's Remote IO, and how the physical layer of the network...
Replies
5
Views
954
Does anybody know if there is an actual limit on the number of drives that can be connected via RIO? I think I've heard there is a theoretical...
Replies
4
Views
1,450
Would it be possible to have multiple PLC's on the same DH+ RIO network. Each controlling separate IO.
Replies
1
Views
2,205
We have an SLC5/05 PLC that has a RIO scanner card that attaches to the IO blocks on fixture and a MARIO Board inside robot cabinet. The mario...
Replies
1
Views
1,716
We have DH+ network on 6 PLC5. We have RSView32 as a HMI. Previously we link HMI with DH+ network by 1784-KT card but we have a problem on some...