Beckhoff EL1002 Wiring details: Few questions

pramod_gr

Member
Join Date
Jun 2010
Location
Bangalore
Posts
7
I would be using Beckhoff EL1002 Digital input module for my EMO switch. Attached is the connection details of the same. I presume that the 24V DC is available internally from EL1002. I would be using it along with EK1100. Can anyone let me know if the connection mentioned below is correct or do i have to connect 24V from an external power supply.
 
The wiring would be correct for a typical switch, but would you want the PLC to be in control of a potentially dangerous emergency stop?

A better practice is to also have it switch off outputs through hard wiring or completely shut down control.
 
The way I interpret his drawing is that he is picking up the 24VDC bus at terminal 2, passing through the switch, and then to Input 1 on terminal 1.

You are right. I have somehow confused terminal numbers and terminal designators.

Pramod, please disregard my statement. I was wrong.
 

Similar Topics

I would be using Beckhoff EL1002 Digital input module for my EMO switch. Attached is the connection details of the same. I presume that the 24V DC...
Replies
0
Views
1,687
Hi, I'm trying to import a Rockwell/AB EDS to Beckhoff but I'm not sure how to import/install the EDS. It is a PowerFlex 525 EDS. Is there a way...
Replies
1
Views
118
I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
135
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
1,090
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
Replies
0
Views
111
Back
Top Bottom