3
Looking to put a current transducer shunt on a line with the mV reading going directly to a PLC. Using the ABB S800 modules.

From what I understand though the current shunt reading is in milivolts.
The I/O modules I see have things like:

Q9Msrnz.png


Does this "nominal input range" 0(2) - +10V mean the minimum input voltage it can take is 2V? And thus my current shunt won't work if input into this.

Does anyone familiar with this range of products know which I/O module I should be feeding mV current shunt readings into:
 
Does this "nominal input range" 0(2) - +10V mean the minimum input voltage it can take is 2V?
No, it means that the voltage input range is either 0-10Vdc or 2-10Vdc. The 2-10Vdc range is sometimes encountered when a 4-20mA signal is driven through a 500 ohm resistor creating a 2-10Vdc signal.

Looking to put a current transducer shunt on a line with the mV reading going directly to a PLC.
Whether this module works satisfactorily will depend upon how many millivolts your shunt provides.

If the shunt provides only 50mV, that's 0.05V which is only 0.5% of the 10V input span. The 12 bit span has a resolution of 1:4000, so 0.5% of 4000 = 20 bits.

A 50mV shunt span will be resolved with only 20 bits, a step change for every 2.5mV.

But you haven't said what the potential span of the shunt output is.

The AI835/AI835A Thermocouple/mV Input Module is designed to handle mV signals up to 75mV:

The AI835/AI835A Thermocouple/mV Input Moduleis part of the S800 I/O. It provides 8 differential input channels for Thermocouple/mV measurements. Measurement ranges configurable per channel are:
-30 mV to +75 mV linear, or TC Types B . . .
 

Similar Topics

I am experimenting with a very simple program for testing purposes and not getting any movement from the servo motor. The attached program...
Replies
6
Views
1,800
Hello, Hoping there is someone out there knowledgeable with GE S2K series motion controllers. The actual model is an IC800SSI104D2-DE. It is...
Replies
0
Views
1,113
I'm looking at bidding what seems to be some standard pump controls for a local levy. The one thing that is giving me a bit of grief is this part...
Replies
19
Views
5,607
Some time has passed since this thread about Thingworx. Any update in light of news of the Rockwell $1B investment in PTC. This video glazes over...
Replies
4
Views
2,558
I installed Drivewindow Light 2 v.2.92 and am having trouble getting fully connected to an ABB ACH 550 drive. I made an adapter following this...
Replies
3
Views
5,815
Back
Top Bottom