With a 0V-10V analogue input card is the positive common or is the negative common? Is there a analogue input card that reads a switching negative sort of like a npn analogue input card i suppose?
 
anything Steve you tell me ! How about hitachi or Mitsubishi oh and can you briefly explain the bipolar modules! thankyou
 
An analog input module reads the potential difference between two terminals. A bipolar module will have the ability to report both positive and negative potential differences.

In a twelve-bit module, a positive voltage might show up in the PLC as an integer value between zero and +4095, a negative voltage as an integer value between zero and -4095.

The spec sheets for the module you're evaluating should tell you if it can handle negative voltages.
 
Most commonly the -Ve side is expected to be grounded, to the same point as the -Ve side power supply and the card gives more stable results this way , lower noise ( you also get better results if ground both sides of unused analog inputs on same card) but both should be able to float so long as they dont float higher than the isolation value of the card.
 

Similar Topics

I have just started commissioning an et200m link module over profibus, I have a number of analogue input cards that I can view using a vat table...
Replies
4
Views
1,773
Hi its been a while since I did any plc programming & things have moved on somwhat Im looking for some programming examples for the mitsi alpha...
Replies
7
Views
4,744
I need to upgrade an existing TSX 3721 Micro with 24 TC inputs and 8 4-20mA inputs. The controller will not allow more than 4 analogue boards even...
Replies
1
Views
2,545
I've been using PLCs for quite a while but have not managed to get my head around the various ways that analogue signals can be tied into...
Replies
14
Views
41,127
How can I adjust my RTD readings into an A-B plc i/o card? If I test the RTD by inserting into a temperature bath, how can I adjust A-B reading to...
Replies
5
Views
7,410
Back
Top Bottom