allen bradley micro logic 1200 blowing input fuse

utahspud

Member
Join Date
May 2020
Location
washington
Posts
2
I have an allen Bradley micro running a fan in an industrial paint mixing facility. The input fuse is 3a. The system will run fine for a bit and then all of a sudden the input fuse will blow. There is only .22 amps on on the fuse with the fan running. Anyone have any ideas on what could be spiking in the controller to cause the fuse to blow?
 
yes the fuse is the input to the plc
Its a 1200 series micro logic.
120v
Fuse is ATQR3. 3a


I cant ever see more then .22 amps when I am testing. Found out the problem has been going on for a long time, they have just been replacing the fuse daily.
 
The inrush current at power up can be quite high for a few milliseconds. The book says 25a for 8ms. You have a time delay fuse, so that is not likely to be the case. Does the input power get turned off an on frequently and if so does the fuse blow when first powered up?

Is that circuit going ONLY to the PLC power supply terminal?

Also, some models have a small 24 volt power supply built into the PLC that can be used to power sensors/switches. Is anything wired to the PLC 24 volt power supply terminals?
 

Similar Topics

This unit was removed from one project where it had perfomed nicely. Wired into simulator and we have no signs of life no LED,s lit power...
Replies
2
Views
950
Hello Everyone, Hope you all are doing well. I am new to the PLC and communication protocols used in PLC. I am currently stuck with Allen...
Replies
47
Views
13,917
Hi all, I have problem that I could do with some help with: I have a setup consisting of an Allen Bradley Micro 820 controller, Panelview 800 and...
Replies
6
Views
3,068
Found a couple of old unused Micro 810s with lcd displays in the miscellaneous section. Don't ever use ccw or indeed any Allen Bradley, but...
Replies
12
Views
4,194
Hi guys, I need to add 2 x 1769-IF4 and 1 x 1769 OW16 output card into an existing Micro 1400 Series A PLC. It has already has 3 expansion...
Replies