AC Transducer Bench Testing

afm

Member
Join Date
Aug 2023
Location
Tennessee
Posts
88
Hi all,

I have a AC current transducer that I want to bench test to ensure I am getting a 4-20mA output. I am using a AE001 unit. It is very simple, with only an M12 cable that I have wired the following way: L+ on 24V supply of PLC (brown wire) , L- on GND of PLC (blue wire) , and IO-Link output of PLC (black wire). I am using an X20DS4387 IO-link module. When I wire and power my PLC, I get no output when live monitoring my PLC. I am unsure how to externally bench test this as there are no terminals on this CT like other transducers I have worked with.
(Current sensor with IO-Link)

For context I previously used an ACT050-42L-F with an IFM DP2200 wired the same way to my PLC that worked well. With no load, I see an output of 4.0 mA. My goal is two eliminate these two components with this one sensor. I am new to instrumentation so all advice is appreciated. Thanks!

At the moment I do not have a lot of testing/measuring instruments on me aside from a basic MM, basic signal generator, and a variable PS for bench testing. See below:

https://www.amazon.com/Adjustable-Generator-Simulator-Controller-Calibration/dp/B0991ZSBHJ/
https://www.amazon.com/SHNITPWR-Universal-Adjustable-Switching-100V-240V/dp/B08N4R48LJ/
Modify message

« Last Edit: Today at 04:51:38 pm by am1 »
 
Do you have the 4-20 ma signal on the white wire? Why not simply use that signal to the PLC (analog input). What PLC do you have?
 
Its a B&R X20CP0483 system. Unfortunately the only analog input module I have is for +/-10V signals (X20AI4222). I have this IO-Link module (X20DS4387) that can operate as IO-link or standard input/outputs, so I wanted to see if it would be possible to get my output while eliminating the converter. But I guess a convertor is needed if I am using this hardware?
 

Similar Topics

I have a set of these: https://www.i-s.gr/files/ND%20Clamp-on%20CT%20Brochure.pdf Specifically M1.UM which outputs Voltage. I am looking to use...
Replies
2
Views
689
Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
Replies
4
Views
1,114
Has any used a ballistic pressure transducer with a PLC? I am not sure if it will capture the event that I need to use as a control. The device...
Replies
2
Views
1,100
I am updating controls on a leak tester, from a SLC 5/02 to Compact Logix. The SLC used a DDV instruction to help scale a differential pressure...
Replies
17
Views
4,481
I have a Pump 1 Current in my Local:5:I.Ch00Data address. I need to add this to my ladder logic program as the goal is to have it eventually be a...
Replies
2
Views
1,479
Back
Top Bottom