We have simulated the complete set up with for ABB ACS800 Drive outside panel.
But we keep getting alarm “ DC UNDER VOLTAGE “
On Display we can see DC BUS BAR VOLTAGE KEEP fluctuating BETWEEN 160 to 280 voltage.

Can any one suggest HOW DC bus voltage is sensed by AINT-02 C card in ACS800

Thanks
 
Last edited:
Measure the line voltage into the drive at U1 V1 & W1 and make sure it is within the drive limits.
What is your drive rated for input line volts?
 
The ACS800's lowest functional DC voltage is around 265vdc and that would be for a unit built specifically for 208VAC input voltage.

The formula to determine this is (minimum listed input voltage x .9 x 1.414).

Your simulator should determine Low Voltage Alarm using the same values.
 

Similar Topics

Is it possible to connect a PC to the mini console's RJ12 connector? use an RJ12/DB9 cable?
Replies
1
Views
999
Hi ,, Could you please any one help me, How to run abb acs 800 drive as encoder less mode by setting parameters on parameter screen.
Replies
2
Views
1,892
Hi everyone, i know its not the right place for that sort of question , but i need help so please excuse me . i have an ABB acs 800 vfd and i am...
Replies
2
Views
4,391
Hi Everybody I hope someone could clarify me on this issue. We have an ACS 800 ABB Drive (cabinet built) for 400 kW motor. When it is powered...