AB Safety Input Module 1734-IB8S Loses Configuration

Sensorless

Member
Join Date
Feb 2021
Location
Ontario
Posts
7
Hello All,

So a weird issue has been happening for me with an in service point I/O drop. I have a 1734-aentr com module, 3 standard I/O cards, a power supply module and then 4 safety I/O cards. The issue I am having is that the 1st and 3rd (Slot 4 & 6) safety I/O cards are losing their configuration which results in an E-Stop being triggered.

The fault code that displays is #0010 with a blinking green MS indicator.

Has anyone had an issue like this with their 1734 safety I/O??

All I have to do is cycle power to the drop and then it starts working again.
 
There is a KB article I found a while back that explains series B IB8S modules have had some manufacturing issues that cause intermittent connection faults. KB BF27095, access level: Everyone

Edit: I found this after troubleshooting a field issue over the phone. Replacing the module resolved it.
 

Similar Topics

Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
Replies
0
Views
26
I ran into a strange issue the other day. System has been up and running for many months. An analog input channel suddenly reported 0mA. I...
Replies
21
Views
3,377
I have two cards (IB8S/B) on which safety input channel goes to fault about once per day (point status goes to 0). Inputs are related to two...
Replies
2
Views
1,345
Hey! Quick question. Is there a quick and easy way of recurrently move safety inputs to a DINT for example? This is the idea but for obvious...
Replies
4
Views
1,837
Hi all, We tried to setup the hardware onto a 10 slot rack as follows, PS Slot 0: 5580 controller Slot 1: Safety Partner Slot 2: Safe Inp Slot...
Replies
8
Views
2,754
Back
Top Bottom