with 1769 OF4. Setting output to 20ma

If measured with meter at output no device connected get
PLC -- Meter
20ma output

If measured with meter at end device
PLC - Wires - Meter
20ma

If I then connect VFD to the output
PLC -- wires -- VFD
Signal = 16ma
(meter in series measurement and as read by VFD with meter)

If I connect a meter and source using meter 20ma from where PLC is
Meter -- same wires -- VFD
20ma at VFD as read by VFD

anyone seen something like this. Only thing I can think of is faulty output card but can't think of why it would be faulting like this. Any other ideas?
 
What is the load resistance of your VFD?

The card will support 0-600 ohms, in the current mode.

Are you sure the VFD accepts current? Some want voltage.
 
Last edited:
Do you see a similar error if you set the PLC output to 4 mA, assuming this is setup as 4-20 mA?
You are wired to I out 0+ and ANLG Comm? Assuming that you are using output "0". And nothing is wired to V out 0+.
 
Not sure of VFD resistance but I have used same plc/vfd combo before without issue so I am sure that it isn't an native incompatibility issue.

VFD is set to current input.

Plc is set to 4-20 ma
Output set at 4ma - shows 4ma and vfd at 0
Output at 12ma (50%) VFD reference shows 50%/30hz
 

Similar Topics

Hello Guys, I am using 1769-L36ERMS PLC by Rockwell which doesn't let me MOV or COP literal text into string datatype? i very well know the...
Replies
13
Views
408
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
Replies
8
Views
417
looking for the the MAC address for this PLC, I count find it in the front or at any part of the PLC itself. connected to the PLC by USB, showing...
Replies
11
Views
1,774
hello plc professionals , i have a plc AB 1769-l24er and 13 VFD AB 525 and HMI and STRAIX 2000 unmanaged switch .. the LOGIX Designer limiting me...
Replies
6
Views
1,538
Been seeing a high failure rate on these PLC's on 2 of our process. The control power is feed through a APC UPS to a 24VDC power supply to power...
Replies
14
Views
4,042
Back
Top Bottom