AB analog card 1756-IF16 redundant wiring

delforum

Member
Join Date
Jul 2014
Location
US
Posts
7
Hello PLCTalk Friends,

I am interested in connecting one 2-wire loop powered 4-20mA transmitter to two analog input cards. In my program, I will compare the two channels on the different analog input cards to see if one of the cards is receiving a bad signal.

Will using two 1756-IF16 allow me to use all 16 channels for 16 loop powered transmitters this purpose?

My thoughts,
Connect Transmitter + to 24V
Connect Transmitter - to the Card1 Channel IN-0
Connect the Card1 I-RTN-0 to Card2 Channel IN-0
Connect the Card2 I-RTN-0 to RTN
Connect the RTN to 0V

Thank you for your help,
Del
 
question for you, what is a 4-20 ma loop?
what you propose is adding an additional resistor in the loop and will make your results invalid.

you should loop for a 4-20ma signal splitter.
if I am wrong on this, someone please correct me.
james
 

Similar Topics

Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,232
Hello, we chose Allen-Bradley analog card 1756-IF16 for three 4-20mA current inputs for XFMR high side winding temp, low side winding temp and...
Replies
5
Views
2,786
Good Evening , I have a 1756-IF16 Analog Input card already installed in a working ControlLogix Rack. I need to add another Analog 4-20 ma...
Replies
1
Views
2,197
I am looking for information on the proper calibration of an 1756-IF8 analog input card, preferably the wiring of the voltage source. Rockwell...
Replies
10
Views
8,071
I've got this 1756-IF8 card configured for 8 single ended inputs as shown below, but none of the channels are read real values (about 4 ma in the...
Replies
7
Views
2,586
Back
Top Bottom