Hi, I have a compact logix processor with embedded IO but the IO is not responding nor flashing on the self test when boots up. The IO light is just flashing and it does not see the IO in project. Any thoughts? Thanks
 
Sure but even creating a blank project doesn't seem to help. I'm guessing cause of catalogue number embedded IO should automatically be set up and it does appear in the tag database.

Ill sort a copy of project out and post. Thanks for your reply
 
My recollection is that the embedded modules do flash their channel indicator LEDs during startup, so if yours don't do that and are showing a faulted connection to the controller, I would say that they are defective out-of-the-box.

Do you have any expansion I/O modules connected to the POINTBus ? Do those work ?
 
I'm trying to recall if on the face of the PLC there are two power inputs. One would be for processor power and one is for I/O power. If so, then both may need to be powered.
 
Yep there's troubles afoot because I booted up my l16 yesterday and all the controller hardware IO flashes in sequence before point io expansion cards.

Try to reflash the firmware and verify expansion IO cards on 1st page of controller properties is set to correct number of installed point IO cards
 
I know this is an old thread, but i came across the same issue with a 1769-L18ERM-BB1b. I found out that you have to set the proper expansion modules in the controller properties. The default is 8 from a blank project, so if you are not using any additional modules, then it has to be set to 0. Then the IO will no longer claim that its faulted.

Hope this is useful.
 

Similar Topics

I have the exact same issue as the OP in this thread. https://www.plctalk.com/qanda/showthread.php?p=916010 I swapped parts with another L18...
Replies
5
Views
2,849
Hello, I am a bit familiar with PLC programming, but I've never dealt with servo drives before. I am having a hard time even establishing a comm...
Replies
2
Views
1,385
Morning. Usually program on ConytrolLogix hardware platform. Bought a 1769-l18erm-bb1b unit to allow us test out concept here in lab- before...
Replies
12
Views
4,246
I am using studio 5000 v24 software for controlling a servo drive. Kinetix 5500 and using the 1769-L18ERM processor. The module I created the...
Replies
7
Views
4,311
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...