5400 Switches with ETAP architecture

zzl630

Member
Join Date
Oct 2013
Location
Houston,TX
Posts
11
Hi Guys,

Another thread with 5400 switches and ETAPs.
See below the current architecture. I have 6 remote IO boxes, each with a pair of 1783-ETAP1F and 4 AENTR. So I counted a total of 40 nodes in this DLR, seems a lot and makes me worry about the speed and response time. So trying to get a second opinion from everyone.
Q1: Can I config 5400 switches as redundant gateways? Got conflict info from manual and people used it lately
Q2: shall I consider multiple DLR rather than 1 big DLR? There are consideration during startup these remote IO boxes will commissioned by phases.

Capture.PNG
 
This is way over my head, but I would check out Rockwell's Ethernet/IP Capacity tool, which is part of Integrated Architecture builder. Once you start throwing devices in there, it may point out an issue.
 
This is way over my head, but I would check out Rockwell's Ethernet/IP Capacity tool, which is part of Integrated Architecture builder. Once you start throwing devices in there, it may point out an issue.

I checked with a pair of ETAP and 4 AENTR seems ok, not sure if can check the impact on speed with so many nodes.
 
Yes, ring master/supervisor.
There is a little known utility DLR for diagnostic, have you tried that ?.
I am thinking of the same thing, EN2TR as a master, rather than using 5400.
Your ETAPs usage is a little unusual, normally ETAPs are used to bring non-DLR devices into the ring.
40 nodes/50 max.

This may be pertaining to what you have:

Do not configure these features on DLR-enabled ports:
• EtherChannel
• Network Address Translation (NAT)
Resilient Ethernet Protocol (REP)
• Spanning Tree Protocol (STP)
• Parallel Redundancy Protocol (PRP)
• Flex Links
• 802.1x Security
 
Last edited:
Yes, ring master/supervisor.
There is a little known utility DLR for diagnostic, have you tried that ?.
I am thinking of the same thing, EN2TR as a master, rather than using 5400.
Your ETAPs usage is a little unusual, normally ETAPs are used to bring non-DLR devices into the ring.
40 nodes/50 max.

This may be pertaining to what you have:

Do not configure these features on DLR-enabled ports:
• EtherChannel
• Network Address Translation (NAT)
Resilient Ethernet Protocol (REP)
• Spanning Tree Protocol (STP)
• Parallel Redundancy Protocol (PRP)
• Flex Links
• 802.1x Security

No I haven't tried that. Is that the Rockwell's Ethernet/IP Capacity tool previous post mentioned?

I consider using ETAP here firstly as a media converter, secondly create a DLR VS a single switch as single point failure, and third to reduce configuration work since we have a lot of switches to config.

Yes good point, I planned to config G1-G4 ports for REP and the rest ports for DLR.
 
If you take redundancy out of picture, then two Stratix switched on DLR must be configured as a Redundant Gateways because of REP.
ETAP is not compatible with Redundant Gateway and will drop connection on RG switchover.
Besides the ETAP, if redundant controllers are part of the ring, then this is a a valid connection. Publication HIGHAV-RM002 calling it Direct Converged.
The only recommendation is to have switched between two controllers and not separate controllers and IO.
And do not connect ANYTHING else to non-DLR ports of redundant gateways.
 
Last edited:
Thanks for the inputs. I duplicate the architecture in Ethernet/IP Capacity tool to see the performance and seems ok to me.

ENetCap_SS.1.png
 
If you take redundancy out of picture, then two Stratix switched on DLR must be configured as a Redundant Gateways because of REP.
ETAP is not compatible with Redundant Gateway and will drop connection on RG switchover.
Besides the ETAP, if redundant controllers are part of the ring, then this is a a valid connection. Publication HIGHAV-RM002 calling it Direct Converged.
The only recommendation is to have switched between two controllers and not separate controllers and IO.
And do not connect ANYTHING else to non-DLR ports of redundant gateways.

Not sure how accurate the IAB is but when I add those switches it says this switch must be configured as redundant gateway

Capture.PNG
 
In my opinion, you are using ETAPs strictly as media converters, so it should be Ok, but you may need to ask Techsupport.
Redundant Gateway terminology is in relation to the distribution switches. So if only one DLR switch is connected to the distribution then you don't need redundant gateway.
 

Similar Topics

Hello All. I am currently working on a project where the client has specified that we cannot use Allen Bradley materials. As a result I need to...
Replies
6
Views
9,039
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
Replies
3
Views
78
Can someone tell me the major difference between the Stratix 5400 and 5800 series? Looking at the data sheets depending on the part number you...
Replies
2
Views
1,113
Hi all. I am trying to sync my computer time to the time displayed on the switch because the time on the errors and everything else is completely...
Replies
11
Views
2,621
Hi all. I have a stratix 5400 switch connected to a 1756-L83E controller via ethernet and I am trying to monitor the DLR network of the switch...
Replies
11
Views
3,209