Hi all,

I've been without luck flashing a 5069-HSC2xOB4/A module to anything higher than the onboard v1.050 firmware.

Has anyone else had luck with this module, or others in general?

The setup:
  • Controller is a L320ERM with firmware 32.14
  • Module is working, has firmware 1.050, and occupies slot 1
  • No other modules
  • MOD power good
  • SA power good

Approaches and tools tried:
  • Direct Ethernet and USB connections
  • Controller in remote run or program mode
  • Module inhibited in I/O tree
  • Module not inhibited in I/O tree
  • Module removed from I/O tree
  • Module inhibited in I/O tree and manually reset
  • 2.011 / 3.012 with latest ControlFlash
  • 2.011 / 3.012 with latest ControlFlash Plus
  • RSLinx Classic Gateway
  • FactoryTalk Linx
  • 2 hours of phone support with Rockwell (this included all of the above including a factory reset of the controller)

Furthest degree of success:
  • ControlFlash claims the module isn't in the correct mode to accept a firmware update, fails, then provides a pop-up "Manually Reset Module"
  • ControlFlash Plus immediately advances from 'Flashing' to 'Polling for Power-Up', then times out with error "Failed to begin update to the target device.The target device is not in the proper mode to accept an update.Manually Reset module"
 
Last edited:
You have provided all options one could think of. Is it possible that there is an issue in the wiring of 5069-HSC2xOB4/A that causes it to detect a fault that does not allow firmware update? Is the 5069-HSC2xOB4/A wired to the physical IO?
 
So, the only thing I can think that you have not tried is to plug some real IO in case the lack of IO can generate an error condition that prevents flashing new firmware.
 
In the manual: 5069-um006_-en-p.pdf for the compactlogix, on page: 29, it states that the firmware update request is rejected as long as the "Connection running" state is true.
On page 108 it also mentions that the LED on the controller must be flashing green to indicate that the module is powered and with no connection.

I would suggest erasing the program on the PLC(By doing a download and cancelling mid-way, or maybe pull the battery out?), then trying another flash?
Thanks!
-PreLC
 
This only works if the connection is inhibited from the tree as an open connection from the processor along the backplane (even if in program mode) causes the flash to fail
 

Similar Topics

Hello everyone, I am having issues with an output module connected to my 5069-L306ER PLC. The modules I have connected are a 5069-IA16 in slot 1...
Replies
1
Views
720
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
Replies
4
Views
1,684
I have a new L306 CompactLogix running V33 with a 5069-Serial module in order to send data through RS-232 to a Sato S84EX printer. I'm unable to...
Replies
1
Views
1,340
There has been a few posts recently where the 5069-SERIAL module was the topic or at least part of the topic and in those conversations some...
Replies
7
Views
5,306
I know there are modules out there but are there any ASi modules for the 5069 series? I'm not finding any. Has anyone tried using the U71003 from IFM?
Replies
6
Views
1,837
Back
Top Bottom