Meanwell have 24VDC/24VDC power supplies with paralleling lines between them. I use them all the time.

ADM are the distributors in Oz - admtech.com.au. DDR-240B-24 is the one I use. Omron also have power supplies with paralleling but i think they are all 240VAC input supply.
 
Use a DC amp probe to make sure the amp loads and voltages are even, or else you'll overload one of the power supplies. If they aren't even, adjust the voltage output on them until they are.
 
Given the age of the power supply maybe that is giving out slowly.

I’m mostly familiar with Phoenix Contact and they state explicitly whether their power supplies can be paralleled. Most name brand suppliers probably have that on their data sheets.

Or you could replace it with a 40 Amp Quint Power Supply from Phoenix contact which can supply 45 amps if necessary (indefinitely if the temp is below 40C)
 
I agree with the above comments about not running in parallel unless it is rated for it. But on a side note, how is the power supply mounted? The Sola's and many others, are derated by temperature and if they are mounted sideways.
 

Similar Topics

We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
Replies
1
Views
120
is this possible? i have a customer has has a large factory, he has 2 x 800amp supplies coming into the site and would like to switch between...
Replies
8
Views
932
Hey Guys, Can anyone recommend a P/N for 48VDC input, 12VDC output power supply. I tried looking up Phoenix Contact/ RHINO, and wasn't able to...
Replies
3
Views
1,489
Hi all, I was hoping someone could tell me if there's an advantage between using PULS or AB power supplies that are rated for SELV and PELV? I...
Replies
5
Views
2,000
I have an application where I need around 60 Amps of 24V. Most 24V PS go up to 40A, so I need to be able to add them in parallel. Puls power...
Replies
36
Views
10,431
Back
Top Bottom