2 wire NPN sensor wiring, sinking sourcing?

AmazingTrans

Member
Join Date
Nov 2005
Location
Illinois
Posts
38
Hi there,

I have a 2 wire npn sensor. For example in this diagram:
F1172_E2E-X_D1-N_E.jpg


I'm guessing i should connect it to a PLC dc sourcing input as such? Would i need a resistor between the PLC #1 DI to the sensor Collector ?
https://snag.gy/TEpJXM.jpg

ow can i just have the brown wire of the sensor goes to input 1, and black wire goes to common (0 Vdc)? Assuming the PLC sourcing digital input internally already has a resistor?

I always used a 3 wire npn sensor, and wiring is done as such:
Table-3-600x290.jpg
 
Your PLC will act as your load. Depending on what your common point (+ or OVDC) is on your PLC, will determine which wire is connected.

Two wire sensors are known for leakage. Please check the specifications on the sensor to determine the leakage current. Calculate the amount based on the input impedance of the PLC to determine if it will falsely trigger the input.
If it will then you may need resistor.

http://www.plctalk.net/qanda/showthread.php?t=72951
The above thread is similar.

Hope this helps you out.
Regards,
 
Thanks for the reply garry,
the leakage of the sensor i have is approximately 0.7 ma.

And if the plc input i were to use is a sourcing type, such as this: http://sie.ag/2v2jkSc

Based of the spec, the typ input current is at 7ma. Guess it wont work then? but on the other than, it also support 2-wire BERO
 
The specs for the card indicate a value of 7ma to have the card indicate an ON or 1 condition.This means that 10 of these 2 wire sensors. (Leakage 0.7ma) can be used per card common before you will get false signals.

Regards,
 
If you really want to use that sensor, connect it to a small SPDT relay and use the relay contact as your PLC input. That will eliminate the leakage problem for about $10.
 

Similar Topics

We have a stamping press with some prox sensors on the die for slug detection and we just ran into a problem where the output from one of the...
Replies
1
Views
1,324
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
315
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
Replies
1
Views
98
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
Replies
1
Views
1,013
What's everyone use for I/O drawings on new installs. I am trying AutoCad Electrical, but can't download it due to a MS Office application running...
Replies
11
Views
1,340
Back
Top Bottom